Insurance Engineer
REGISTERED
A sprinkler contractor flow tests a fire pump at a large hospital.
Pump rating data of fire pump: Churn: 88.7psi, 1500 gpm @80 psi, 2250 gpm@ 68.6 psi
Here is what was on the test reports:
2010 Pump Test
Discharge Pressure
176, 181, 177
Suction Pressure
84, 115, 153
Net Pressure
72,66,24
Flow GPM
0, 1500, 2250
2009 Pump Test
Discharge Pressure
160,175,175
Suction Pressure
75,110,155
Net Pressure
85,65,20
Flow GPM
0, 1500, 2250
This is what NFPA 25, 2008 says
8.3.5.3 The fire pump assembly shall be considered acceptable if either of the following conditions is shown during the
test:
(1)*The test is no less than 95 percent of the pressure at rated flow and rated speed of the initial unadjusted field acceptance test curve, provided that the original acceptance test curve matches the original certified pump curve by
using theoretical factors.
(2) The fire pump is no less than 95 percent of the performance characteristics as indicated on the pump nameplate.
****************************
8.3.5.4* Degradation in excess of 5 percent of the pressure of the initial unadjusted acceptance test curve or nameplate shall require an investigation to reveal the cause of degraded performance.
***************************************
The pump graph with the report graphs the discharge psi, suction psi and ***** psi. It does not graph the net pump pressure and gpm. The pump test report does NOT list the Churn rating of the pump OR the 150% psi rating of the fire pump.
So what do you think?? Do I have a problem??
Pump rating data of fire pump: Churn: 88.7psi, 1500 gpm @80 psi, 2250 gpm@ 68.6 psi
Here is what was on the test reports:
2010 Pump Test
Discharge Pressure
176, 181, 177
Suction Pressure
84, 115, 153
Net Pressure
72,66,24
Flow GPM
0, 1500, 2250
2009 Pump Test
Discharge Pressure
160,175,175
Suction Pressure
75,110,155
Net Pressure
85,65,20
Flow GPM
0, 1500, 2250
This is what NFPA 25, 2008 says
8.3.5.3 The fire pump assembly shall be considered acceptable if either of the following conditions is shown during the
test:
(1)*The test is no less than 95 percent of the pressure at rated flow and rated speed of the initial unadjusted field acceptance test curve, provided that the original acceptance test curve matches the original certified pump curve by
using theoretical factors.
(2) The fire pump is no less than 95 percent of the performance characteristics as indicated on the pump nameplate.
****************************
8.3.5.4* Degradation in excess of 5 percent of the pressure of the initial unadjusted acceptance test curve or nameplate shall require an investigation to reveal the cause of degraded performance.
***************************************
The pump graph with the report graphs the discharge psi, suction psi and ***** psi. It does not graph the net pump pressure and gpm. The pump test report does NOT list the Churn rating of the pump OR the 150% psi rating of the fire pump.
So what do you think?? Do I have a problem??
Last edited by a moderator: