Another inspection passed by the inspector

Kearney.200 said:
do yo have them remove the panel cover for a final?
If they are present, yes. If no, we do and have been. Not looking for excuses to justify not doing our job.

They don't have a ladder to get us on the roof or into a basement then that's a problem.
 
jar546 said:
The electrical final was signed off by the previous inspector.Any problems with this?

View attachment 1710

Probably trained this guy:

View attachment 1718
110.14 Electrical Connections.

(A) Terminals. Connection of conductors to terminal parts shall ensure a thoroughly good connection without damaging the conductors and shall be made by means of pressure connectors (including set-screw type), solder lugs, or splices to flexible leads. Connection by means of wire-binding screws or studs and nuts that have upturned lugs or the equivalent shall be permitted for 10 AWG or smaller conductors.

Terminals for more than one conductor and terminals used to connect aluminum shall be so identified.

408.41 Grounded Conductor Terminations.

Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.
 