2015 IBC Section 716.5 Fire door and shutter assemblies.
Say you've got a fire door assembly with multiple individual sidelights. The wall is a 1-hr fire partition - a corridor wall. Door is a side hinged door.
It appears the assembly has the following limitations:
A plan reviewer has cited 716.6.7.2 which says "The total area of the glazing in fire-protection-rated window assemblies shall not exceed 25 percent of the area of a common wall with any room." However, this appears to be specific only to fire window assemblies. 716.6 refers glazing in fire door assemblies to 716.5.8. The commentary on 716.6 says "This section covers glazing in fire windows, not fire doors.."
Online commentary on this issue appears limited, but SAFTIFIRST has a few posts that interpret the 25% limitation to include any fire-resistance-rated glazing. For example, see http://safeglassforschools.com/code.../fire-rated-glazing-in-1-hour-exit-corridors/
In the example sketch attached, if the 25% were applicable, the glazed section proposed would be required to be a 1-hr UL 263 assembly to maintain the design intent.
Are Fire Door Assemblies with sidelights and transoms limited only by what has been tested? Or are they also subject to the 25% limitation of 716.6.7.2?
Thanks in advance for your insight.
Say you've got a fire door assembly with multiple individual sidelights. The wall is a 1-hr fire partition - a corridor wall. Door is a side hinged door.
It appears the assembly has the following limitations:
- Required to be tested with NFPA 252 or UL 10C per 716.5.1
- The door vision panel (the glazing in the door itself) is required to be D-20 labeled to the maximum size tested
- Fire door frames with sidelights and transoms are required to be 3/4-hr rated with D-H-OH-45 glazing for 1-hr corridors per Table 716.5 and 716.5.6
- Fire-resistance glazing shall comply with the size limitations of NFPA 80 per 716.5.8.1
- NFPA 80 specified max area of glazing is "limited to maximum area tested" for 3/4-hr applications
A plan reviewer has cited 716.6.7.2 which says "The total area of the glazing in fire-protection-rated window assemblies shall not exceed 25 percent of the area of a common wall with any room." However, this appears to be specific only to fire window assemblies. 716.6 refers glazing in fire door assemblies to 716.5.8. The commentary on 716.6 says "This section covers glazing in fire windows, not fire doors.."
Online commentary on this issue appears limited, but SAFTIFIRST has a few posts that interpret the 25% limitation to include any fire-resistance-rated glazing. For example, see http://safeglassforschools.com/code.../fire-rated-glazing-in-1-hour-exit-corridors/
In the example sketch attached, if the 25% were applicable, the glazed section proposed would be required to be a 1-hr UL 263 assembly to maintain the design intent.
Are Fire Door Assemblies with sidelights and transoms limited only by what has been tested? Or are they also subject to the 25% limitation of 716.6.7.2?
Thanks in advance for your insight.