The 2010 ADA Standards for Accessible Design do require strobes:
215 Fire Alarm Systems
215.4 Transient Lodging. Guest rooms required to comply with 224.4 shall provide alarms complying with 702.
215.5 Residential Facilities. Where provided in residential dwelling units required to comply with 809.5, alarms shall comply with 702.
224.4 Guest Rooms with Communication Features. In transient lodging facilities, guest rooms with communication features complying with 806.3 shall be provided in accordance with Table 224.4.
224.5 Dispersion. Guest rooms required to provide mobility features complying with 806.2 and guest rooms required to provide communication features complying with 806.3 shall be dispersed . . . At least one guest room required to provide mobility features complying with 806.2 shall also provide communication features complying with 806.3. Not more than 10 percent of guest rooms required to provide mobility features complying with 806.2 shall be used to satisfy the minimum number of guest rooms required to provide communication features complying with 806.3.
702.1 General. Fire alarm systems shall have permanently installed audible and visible alarms complying with NFPA 72 (1999 or 2002 edition) (incorporated by reference, see “Referenced Standards” in Chapter 1), . . . In addition, alarms in guest rooms required to provide communication features shall comply with sections 4-3 and 4-4 of NFPA 72 (1999 edition) or sections 7.4 and 7.5 of NFPA 72 (2002 edition).
806.3 Guest Rooms with Communication Features. Guest rooms required to provide communication features shall comply with 806.3.
806.3.1 Alarms. Where emergency warning systems are provided, alarms complying with 702 shall be provided.
If the IBC and ANSI A117.1 don't have similar requirements they don't meet the ADA.