• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Are truncated domes allowed in an accessible parking access aisle?

Yikes

Gold Member
Joined
Nov 2, 2009
Messages
1,684
Location
Southern California
ADA/CBC 11B-502.4 for accessible parking stall access aisles says: "Changes in level are not permitted. Exception: slopes not steeper than 1:48 shall be permitted."

Questions:

1. Are truncated domes in a detectable warning system per ADA / CBC 11B-705 allowed in the striped access aisle? Or do they constitute a "change in level" that is not allowed? Note that the elevation difference is less than 0.25".

1613594228186.png

2. If a dome that is 0.18" high is NOT allowed, then what are the allowable construction tolerances (surface texture) on an accessible stall and access aisle?
 

ADAguy

Sawhorse
Joined
Sep 11, 2013
Messages
5,517
Location
California
This is a grey area up for revision to the CBC this code cycle. Construction tolerance is limited to 2% crossslope max and no vertical rise exceeding 1/4"
 

Yikes

Gold Member
Joined
Nov 2, 2009
Messages
1,684
Location
Southern California
Why in the world would you put truncated domes in an accessible parking stall access aisle. What is the purpose/reason?
Good question. In this instance, the head of the parking stall's striped aisle is the 4th side of a 3-way "T" intersection walkway system. Long story short, this intersection cannot be altered under present circumstances. My concern is that a blind person on the walkway will come to this intersection, and if the intersection is filled with domes, they won't know which of the 3 pathway options is the "hazardous vehicular way".
 

mark handler

Sawhorse
Joined
Oct 25, 2009
Messages
10,931
Location
So. CA
ADA/CBC 11B-502.4 for accessible parking stall access aisles says: "Changes in level are not permitted. Exception: slopes not steeper than 1:48 shall be permitted."

Questions:

1. Are truncated domes in a detectable warning system per ADA / CBC 11B-705 allowed in the striped access aisle? Or do they constitute a "change in level" that is not allowed? Note that the elevation difference is less than 0.25".

View attachment 7508

2. If a dome that is 0.18" high is NOT allowed, then what are the allowable construction tolerances (surface texture) on an accessible stall and access aisle?
IMHO
No, they can interfere with the loading and unloading of wheelchairs and can be a tripping hazard to those using mobility devices and mobility problems.
 

steveray

Sawhorse
Joined
Nov 25, 2009
Messages
8,043
Location
West of the river CT
I can think of a lot of reasons to not have them there, but not one that code would prohibit them from being there...It is not a change and level and they are required on some accessible routes so they are obviously allowed....It does not sound like a raised marked crossing, why are they there at all?
 