AREA REQUIREMENTS

drew melillo

REGISTERED
Joined
Oct 28, 2016
Messages
4
Location
nbc
I have a 53,000 SF floor plate in Type V-A construction.
The maximum is 36,000 SF w/ sprinklers.
I divided it in half with fire walls as per the provisions in Section 706.
Do I now have two separate buildings that require 2 means of egress each?
 
You do not say what occupancy type.

Plus which building code and edition are you in?
 
Your question got more complicated
R-2
4 floors
245 units

Generally the answer is yes

More than likely wherever the rated wall is, there will have to be a door, and more than likely two, swinging opposite each other.

I need to find the section I found the other day, that might throw a problem into your rated wall. Give me a day
 
Use a horizontal exit. An exit that allows occupants to egress from one side of a building to another side through a fire-resistance-rated assembly, such as a fire wall or fire barrier.

Also remember travel distances.
 
Your question got more complicated
R-2
4 floors
245 units

Generally the answer is yes

More than likely wherever the rated wall is, there will have to be a door, and more than likely two, swinging opposite each other.

I need to find the section I found the other day, that might throw a problem into your rated wall. Give me a day




ok not finding the section, I saw the other day, so never mind, unless I stumble across it
 
706.2 Structural stability. Fire walls shall be designed and
constructed to allow collapse of the structure on either side
without collapse of the wall under fire conditions. Fire walls
designed and constructed in accordance with NFPA 221 shall
be deemed to comply with this section.

Que?
 
..... Mark has some good advice, but you can only use horizontal exit for 50% of your exiting typically...
It is the only way large projects are built
Slider-Building.jpg

The use of horizontal exits reduces the number of exit stairs needed by providing additional egress capacity and assists in meeting travel distance limitations.
http://www.koffel.com/news/Publications/Horizontal_Exits-Dream_or_Nightmare.pdf
 
706.2 Structural stability. Fire walls shall be designed and
constructed to allow collapse of the structure on either side
without collapse of the wall under fire conditions. Fire walls
designed and constructed in accordance with NFPA 221 shall
be deemed to comply with this section.

Que?



Just wondering how he is going to meet the section, with the building he is proposing
 
With fire walls. Rated expansion joints at the "walkway" penetrations [openings]
240929c6-eabb-4e80-99ea-a8b435f7d5b9.jpg

Note: this detail is not totally correct, Does not meet the fire rating or the smoke and draft and fire stop req. But shows the separation.
 
Last edited:
Follow-up question: is it possible to have a 2-hour single-stud fire wall (fka area separation wall) that can still have a floor collapse on one side without damaging the structural integrity of the wall itself?
How would you do the floor/wall junction detail for WP3910 (below)?
2HourSTC50to54StaggeredStudPartition-600x776.png
 
You wouldn't....just like Mark's detail, it has a note on the drawing "allowing collapse", but in reality it won't....You can't attach a floor to a firewall...
 
Follow-up question: is it possible to have a 2-hour single-stud fire wall (fka area separation wall) that can still have a floor collapse on one side without damaging the structural integrity of the wall itself?
How would you do the floor/wall junction detail for WP3910 (below)?
2HourSTC50to54StaggeredStudPartition-600x776.png

Apparently it's possible; see example below.

Yikes what is fka?

Capture.PNG

http://www.uspconnectors.com/pdf/connectors/FWH-sales-sheet.pdf

https://www.strongtie.com/products/go/connectors/firewall-solutions
 
Thanks Francis!....I don't know that I am completely on board with that, but good to look at...

706.2 Structural stability. Fire walls shall have sufficient
structural stability under fire conditions to allow collapse of
construction on either side without collapse of the wall for the
duration of time indicated by the required fire-resistance rating
or shall be constructed as double fire walls in accordance
with NFPA 221.

Unless 221 has some supporting info, tying a floor system into each side of a double stud wall is no bueno to me...
 