• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Article 250

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,051
Location
Somewhere Too Hot & Humid
Resistance. Buried or driven electrodes shall, if practicable, have resistance to ground not to exceed 25 ohms. If the resistance is not as low as 25 ohms, two or more electrodes in parallel shall be used.

Installation. ...................... Each electrode shall be separated at least 6 feet from any other electrode,...................

1947 Edition of National Electrical Code
 
The first edition of the code to contain the 25-ohm section was the 1918 edition. Also in the 1918 edition, the first allowance for pipe electrodes became code. The original requirement permitted a minimum of a 1-in pipe with no less than 4-ft² of surface to exterior soil. The 1923 edition added the driven rod.
 
Since measuring the resistance is impractical, it is a poorly written code section. Much better to remove the resistance provision.
 