I'm working on a 70 unit assisted living facility (I-1) and wanted to verify a couple items pertaining to the resident unit accessibility.
- 2006 IBC (2007 Kentucky Building Code) requires at least 4% of units be accessible with the remainder being Type B. If we make every unit accessible then we are above and beyond code requirements and the Type B part does not apply correct? We would like to make all units accessible or easily converted with minor cost and labor.
- Table 1107.6.1.1 specifies a minimum required number of Roll-In units and accessible units but If I'm reading it correctly it only applies to Group R buildings?
- Assuming the above are there any requirements for a percentage / number of roll-in showers for an I-1 building? The owners expressed some concern over having a curb at the showers and would like to use fully ADA compliant showers (transfer or roll-in.) Based on what I've found in IBC & ANSI a transfer shower is acceptable at all locations but before I make a lot of changes to the plans I'd like to be sure that what we are designing is correct