Has any one done an atrium recently?? Using the 2012 IBC?
If so, just wondering if a glass door was used, how it was protected by yhe fire sprinklers?
Exception: A fire barrier is not required where a glass wall forming a smoke partition is provided. The glass wall shall comply with all of the following:
1. Automatic sprinklers are provided along both sides of the separation wall and doors, or on the room side only if there is not a walkway on the atrium side. The sprinklers shall be located between 4 inches and 12 inches (102 mm and 305 mm) away from the glass and at intervals along the glass not greater than 6 feet (1829 mm). The sprinkler system shall be designed so that the entire surface of the glass is wet upon activation of the sprinkler system without obstruction;
1.1. The glass wall shall be installed in a gasketed frame in a manner that the framing system deflects without breaking (loading) the glass before the sprinkler system operates; and
"""""""""1.2. Where glass doors are provided in the glass wall, they shall be either self-closing or automatic-closing.""""""
ALSO, this provison is not in the 2009 IBC or earlier,
So were glass doors allowed prior to 2012 IBC????
If so, just wondering if a glass door was used, how it was protected by yhe fire sprinklers?
Exception: A fire barrier is not required where a glass wall forming a smoke partition is provided. The glass wall shall comply with all of the following:
1. Automatic sprinklers are provided along both sides of the separation wall and doors, or on the room side only if there is not a walkway on the atrium side. The sprinklers shall be located between 4 inches and 12 inches (102 mm and 305 mm) away from the glass and at intervals along the glass not greater than 6 feet (1829 mm). The sprinkler system shall be designed so that the entire surface of the glass is wet upon activation of the sprinkler system without obstruction;
1.1. The glass wall shall be installed in a gasketed frame in a manner that the framing system deflects without breaking (loading) the glass before the sprinkler system operates; and
"""""""""1.2. Where glass doors are provided in the glass wall, they shall be either self-closing or automatic-closing.""""""
ALSO, this provison is not in the 2009 IBC or earlier,
So were glass doors allowed prior to 2012 IBC????