We are doing an addition that will have a 4:12 roof. It ends up having about 24" clear vertical height from the top of the ceiling joists to the bottom of the roof rafters. Per R807.1 we don't need to have an attic access as the vertical height in the attic is less than 30" however we want to have one anyway. The addition is a master bedroom with a 2' wide x 10' long closet and a master bathroom. We don't want to have the access in the bedroom for esthetic reasons and are thinking of putting it in the closet. I don't think this will comply with being readily accessible but since we don't even need one would think it wouldn't matter. Any opinions on this would be appreciated. Also any opinions on whether an attic access generally in a closet (not a walk in as there's plenty of room in a typical walk in closet) would be allowed for future reference as this issue comes up repeatedly.
R807.1 Buildings with combustible ceiling or
roof construction shall have an attic access opening to attic
areas that exceed 30 square feet (2.8 m2) and have a vertical
height of 30 inches (762 mm) or greater. The vertical height
shall be measured from the top of the ceiling framing members
to the underside of the roof framing members.
The rough-framed opening shall not be less than 22 inches
by 30 inches (559 mm by 762 mm) and shall be located in a
hallway or other readily accessible location. When located in a
wall, the opening shall be a minimum of 22 inches wide by 30
inches high. When the access is located in a ceiling, minimum
unobstructed headroom in the attic space shall be 30 inches
(762 mm) at some point above the access measured vertically
from the bottom of ceiling framing members. See the California
Mechanical Code for access requirements where mechanical
equipment is located in attics.
R807.1 Buildings with combustible ceiling or
roof construction shall have an attic access opening to attic
areas that exceed 30 square feet (2.8 m2) and have a vertical
height of 30 inches (762 mm) or greater. The vertical height
shall be measured from the top of the ceiling framing members
to the underside of the roof framing members.
The rough-framed opening shall not be less than 22 inches
by 30 inches (559 mm by 762 mm) and shall be located in a
hallway or other readily accessible location. When located in a
wall, the opening shall be a minimum of 22 inches wide by 30
inches high. When the access is located in a ceiling, minimum
unobstructed headroom in the attic space shall be 30 inches
(762 mm) at some point above the access measured vertically
from the bottom of ceiling framing members. See the California
Mechanical Code for access requirements where mechanical
equipment is located in attics.