• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Attic Bedroom Egress Window

tag

GREENHORN
Joined
Dec 26, 2016
Messages
6
Location
NYC
Hi Everyone.

What is the maximum distance from grade to an egress window sill? And where does this come up in the code?

I have asked a number of people but they can't tell me where in the code it is specified. Is it even addressed in the residential code?

thank you and happy holidays.
 
Just meet this


Emergency escape and rescue openings shall open directly into a public way, or to a yard or court that opens to a public way
 
Firefighters can put a ladder up

Occupants can wait for firefighters, have their own ladder, hang outside till someone shows, or jump
 
I'm not a fan of heights so that doesn't look fun to me.

I was advised by a building inspector that there was a maximum height drop of 14ft. an architect that I know said the same (maybe a coincidence because they worked in the same town). when I asked him where in the code that came up, he couldn't tell me then tried calling a few other architects he knew.. no one had the answer..


I've spent wayy to much time trying to verify a rule someone else said existed but had no proof of.
 
I'm not a fan of heights so that doesn't look fun to me.
I was advised by a building inspector that there was a maximum height drop of 14ft. an architect that I know said the same (maybe a coincidence because they worked in the same town). when I asked him where in the code that came up, he couldn't tell me then tried calling a few other architects he knew.. no one had the answer..
I've spent wayy to much time trying to verify a rule someone else said existed but had no proof of.
There is no "height to grade" requirement. in the IBC or IRC.
http://codes.iccsafe.org/app/book/content/2015-I-Codes/2015 IRC HTML/Chapter 3.html
See section R310.2.2
 
Last edited:
Last edited:
So is it code?
Or information

According to the Bulletin:
"What does the code require?
All of the above referenced codes require that any sleeping room, up to four stories in height, must have a secondary means of escape. A window is an acceptable means of escape if within 20 feet of grade."

Must be a state thing.....
 
Great question, made me blow the dust off my code books. Made me look!

Mark, great research.

With the individual government entities that Mark has noted, makes you wonder if a required distance ever was part of any code change proposal and if it was, what was the reason for denial?
 
IBC 1029.1 requires sleeping rooms below the 4th story to have emergency escape and rescue openings. This would imply that some egress windows are expected to be more than 15 or 20 ft. above grade.

IRC R310.1 requires all sleeping rooms to have emergency escape and rescue openings, however I think the IRC is limited to 3 story residences.
 
R101.2 Scope.
The provisions of the International Residential Code for One- and Two-family Dwellings shall apply to the construction, alteration, movement, enlargement, replacement, repair, equipment, use and occupancy, location, removal and demolition of detached one- and two-family dwellings and townhouses not more than three stories above grade plane in height with a separate means of egress and their accessory structures """ not more than three stories above grade plane in height. """"





RB] STORY. That portion of a building included between the upper surface of a floor and the upper surface of the floor or roof next above.

[RB] STORY ABOVE GRADE PLANE. Any story having its finished floor surface entirely above grade plane, or in which the finished surface of the floor next above is either of the following:

1. More than 6 feet (1829 mm) above grade plane.

2. More than 12 feet (3658 mm) above the finished ground level at any point.



So are you limited to 12 foot rooms????

Seems like I have seen houses with stories higher than that??
 
IBC 1029.1 requires sleeping rooms below the 4th story to have emergency escape and rescue openings. This would imply that some egress windows are expected to be more than 15 or 20 ft. above grade.

IRC R310.1 requires all sleeping rooms to have emergency escape and rescue openings, however I think the IRC is limited to 3 story residences.

Yes, IRC does limit R class to 3 stories. In NY, we are running on the 2015 IRC with some edits. Prior, we were going off of the 2006 IRC which is when I first heard this unconfirmed rule.

R101.2 Scope.
The provisions of the International Residential Code for One- and Two-family Dwellings shall apply to the construction, alteration, movement, enlargement, replacement, repair, equipment, use and occupancy, location, removal and demolition of detached one- and two-family dwellings and townhouses not more than three stories above grade plane in height with a separate means of egress and their accessory structures """ not more than three stories above grade plane in height. """"

RB] STORY. That portion of a building included between the upper surface of a floor and the upper surface of the floor or roof next above.

[RB] STORY ABOVE GRADE PLANE. Any story having its finished floor surface entirely above grade plane, or in which the finished surface of the floor next above is either of the following:

1. More than 6 feet (1829 mm) above grade plane.

2. More than 12 feet (3658 mm) above the finished ground level at any point.



So are you limited to 12 foot rooms????

Seems like I have seen houses with stories higher than that??

12 feet is nothing, 9 ft ceiling, 14inches for meat between 1&2, that leaves you with less than 2ft from floor to sill on L2.. 10 foot ceiling and your egress windows will need to be tempered and on the floor. FUN!
 
  • Like
Reactions: cda
The Story Above Grade Plane is a way to distinguish between basements (which don't count towards the 3 story limit) and stories.

Years ago I worked for a firm which designed large houses on the coast. The FEMA flood level was 12 ft., so what would have been a 3-story house on piers became a 4 story house that had to meet the IBC instead of IRC.
 
I'm happy to see someone in the State has a sense of humor.. I reached out to New York State because another local inspector said there is a height limitation but could not recall where it stated such a thing or what exactly the height was..


The response I got from NYS..


NYS DOS said:
“R310/311 does not talk about exterior height limitations.”


Hmmm… what do you think that means, when the code is silent on something?
 
Huge thanks to everyone!

Solved. There was a 14ft fall requirement but that only applied to existing dwellings that only received a sprinkler system in the existing finished attic space and along the path of egress..

R313.5.1 - Existing dwellings.
Alterations to an existing
attic which create a building height of three stories above
grade shall be permitted in conformance with Section
AJ604.3 of Appendix J.


2010 NYS code, Appendix J, section 604.3
J604.3.3.2 - An emergency escape and rescue opening,
meeting the requirements of Section R310, located
directly above a roof or other structural
appurtenance from which access to grade does not
exceed a vertical distance of 14 feet.
 