Hi there,
I wanted to see if I can get your take on the 1/300 nfva exception for attics. When it comes to calculating vents for small attic spaces I am getting hung up specifying a vent that fits within the upper vents 40-50% limit.
For example:
Thanks in advance for any comments!
I wanted to see if I can get your take on the 1/300 nfva exception for attics. When it comes to calculating vents for small attic spaces I am getting hung up specifying a vent that fits within the upper vents 40-50% limit.
R806.2 Minimum Vent Area. The minimum net free ventilation area shall be 1/150 of the vented space.
Exception: The minimum net free ventilation area shall he 1/300 of the vented space provided one or more of the following conditions are met:
...2. Not less than 40 percent and not more than 50 percent of the required ventilating area is provided by ventilators located in the upper portion of the attic or rafter space.
For example:
- Attic over a porch is 123 s.f.
- At 1/300 the required total venting area is .41 s.f.
- The upper vents would need a maximum of .205 s.f. nfva.
Thanks in advance for any comments!