Attic ventilations 24" OC

jar546

CBO
Joined
Oct 16, 2009
Messages
13,000
Location
Not where I really want to be
What say ye' about this. What is your opinion?

IMG_3574.jpg
 
My take on it too. If you have the correct amout of attic ventilation, even if it's coming from baffles, all you need is X amout of ventilation. If you have turbines then that amout even goes down farther. I bet this installation meets code.
 
If in doubt have the contractor show the calculations for the net free area of the vents T&B
 
This is a tough one. My brain is saying this is probably a good solution, but my second thought was that it does not meet the code requirements for clearances.

"R806.3Vent and insulation clearance. Where eave or cornice

vents are installed, insulation shall not block the free flow of

air. A minimum of a 1-inch (25 mm) space shall be provided

between the insulation and the roof sheathing and at the location

of the vent."

There is not 1" of clearance provided in all locations due to the shape of the baffle.
 
I think it meets the intent of the code...which is to provide the proper amout of ventilation to the attic. There is not one single building built in the United States that is built completely to the code as written.
 
Can't tell if they have the proper separation or not. Besides H-clips are not required.
 
There is no way to evaluate from the picture how much ventilation is required. I think the intent of the code is met with the way they protected the openings in the eave vents so that they are not blocked.
 