How many KW of heat? and what size conductors on the SE?steveray said:OK...I got a minute now and noone else is biting......Cu to Al conductors without a proper connector, condensate pump wired direct to SEU for air handler, no grounding for pump or metallic box, the j-box is fastened to the equipment where the maker says not to.....Ohh no disconnect either....It'll take me a bit to get NEC sections, but I will if I get a chance....
I was thinking sizing also. And I also would be willing to bet there was no EC involvedDennis said:I would want to know what size conductors and see if the box is legitimate. Where is the disconnect and if there is a disconnect why not go directly into the unit. Looks like the ec didn't want to buy copper down to the unit. What size kw- what size breaker-- it looks like this unit needs to circuits run to it- not one
If you flip the lid left to right the arcs line upgfretwell said:There must have been something else going on before because those arcy sparkies on the cover don't seem to line up with the wires and I don't see any smoke on them.
I agree.....Gregg Harris said:These are good example why a mechanical contractor should also be required to hold an electrical masters or sub to one.