Good morning Everyone,
I have a project that was fabricated and installed at a private condo complex that serves off campus housing near a university in Pennsylvania. The code is the 2015 ICC swimming pool code as adopted. This keeps people out of the outdoor swimming pool area.
When we designed the project we had the issue that the fence would be having guards next to them because this is a raised patio area. Hence you walked up stair flights between two buildings to the pool level above. The guards on the stair flights and the fence would intersect. Thus the guards created an issue with the clear zone requirements and the 45" clear zone requirements.
So to address this we took the minimum guard height of 42" and then added 46" to set our minimum barrier height. This creates the 45" required clear zone at the top of the barrier, rather than the bottom of the barrier which could not be obtained because of the required guards.
In doing this we ended up with a 88" high barrier. So to breakup the height we added a stiffener horizontal at 34 inches above the ground level which creates a 54" vertical clear zone between the 2 horizontal channels.
Once the panels got away from the guards and gates we reduced the height of the barrier panels to 79" overall which is the 34" lower with a 45" upper.
The breakdown of the base design is shown below.
Currently the inspection turned out a violation notice where the AHJ is requesting that the vertical spacing below the 34" be reduced to less than 1-3/4" because it creates a ladder effect of being able to climb up to the 2nd horizontal (at 34") and that this was not allowed at all in the lower portion of the barrier. They might also be talking about the less than 4" spacing's in the upper panels which is over 1.75" and which we have the 45" clear heigth covered, but I am not sure on that, just that they are saying the 45" clear zone needs to be on the lower portion and not allowed on the upper portion.
I have not been able to discuss longer than a minute or so on the phone yet with them and I sent them the below diagram this morning and are waiting for a replay. But in the mean time I am reaching out to get input from my peers on this and see your comment.
I look forward to your comments and will answer any questions one might have.
I have a project that was fabricated and installed at a private condo complex that serves off campus housing near a university in Pennsylvania. The code is the 2015 ICC swimming pool code as adopted. This keeps people out of the outdoor swimming pool area.
When we designed the project we had the issue that the fence would be having guards next to them because this is a raised patio area. Hence you walked up stair flights between two buildings to the pool level above. The guards on the stair flights and the fence would intersect. Thus the guards created an issue with the clear zone requirements and the 45" clear zone requirements.
So to address this we took the minimum guard height of 42" and then added 46" to set our minimum barrier height. This creates the 45" required clear zone at the top of the barrier, rather than the bottom of the barrier which could not be obtained because of the required guards.
In doing this we ended up with a 88" high barrier. So to breakup the height we added a stiffener horizontal at 34 inches above the ground level which creates a 54" vertical clear zone between the 2 horizontal channels.
Once the panels got away from the guards and gates we reduced the height of the barrier panels to 79" overall which is the 34" lower with a 45" upper.
The breakdown of the base design is shown below.
Currently the inspection turned out a violation notice where the AHJ is requesting that the vertical spacing below the 34" be reduced to less than 1-3/4" because it creates a ladder effect of being able to climb up to the 2nd horizontal (at 34") and that this was not allowed at all in the lower portion of the barrier. They might also be talking about the less than 4" spacing's in the upper panels which is over 1.75" and which we have the 45" clear heigth covered, but I am not sure on that, just that they are saying the 45" clear zone needs to be on the lower portion and not allowed on the upper portion.
I have not been able to discuss longer than a minute or so on the phone yet with them and I sent them the below diagram this morning and are waiting for a replay. But in the mean time I am reaching out to get input from my peers on this and see your comment.
I look forward to your comments and will answer any questions one might have.