Pennsylvania's removal of sprinkler language:
(g) Automatic fire sprinkler systems in one-family and twofamily
dwellings.--
(1) Section R313.2 (relating to automatic fire sprinkler
systems in one- and two-family dwellings) of the
International Residential Code (2009 edition), and any
successor triennial revisions, is excluded from this act and
shall not be part of Chapter 3.
(2) A builder of a one-family or two-family dwelling
subject to the International Residential Code shall, at or
before the time of entering into the purchase contract, do
all of the following:
(i) Offer to a buyer the option to install or equip,
at the buyer's expense, an automatic fire sprinkler
system in the building or dwelling unit designed and
installed in accordance with the provisions of section
R313.2.1 (relating to design and installation of
automatic fire sprinkler systems) of the International
Residential Code (2009 edition).
(ii) Provide the buyer with information which
explains the initial and ongoing cost of installing and
equipping an automatic fire sprinkler system in the
building or dwelling unit.
(iii) Provide the buyer with information, as made
available by the State Fire Commissioner on the agency's
Internet website, on the possible benefits of installing
an automatic sprinkler system.
TJI Floor Protection:
(H) FIRE PROTECTION OF FLOORS.--
(1) EXCEPT AS SET FORTH IN PARAGRAPH (2), A FLOOR
ASSEMBLY NOT REQUIRED IN THE INTERNATIONAL RESIDENTIAL CODE,
OR ITS SUCCESSOR BUILDING CODE, TO BE FIRE-RESISTANCE RATED
SHALL BE PROVIDED WITH A 1/2-INCH GYPSUM WALLBOARD MEMBRANE,
5/8-INCH WOOD STRUCTURAL PANEL MEMBRANE, OR EQUIVALENT, ON
THE UNDERSIDE OF THE FLOOR FRAMING MEMBER.
(2) PARAGRAPH (1) SHALL NOT APPLY TO ANY OF THE
FOLLOWING:
(I) A FLOOR ASSEMBLY LOCATED DIRECTLY OVER A SPACE
PROTECTED BY AN AUTOMATIC SPRINKLER SYSTEM IN ACCORDANCE
WITH SECTION P2904, NFPA13D OR OTHER EQUIVALENT SPRINKLER
SYSTEM APPROVED BY A MUNICIPAL CODE OFFICIAL.
(II) A FLOOR ASSEMBLY LOCATED DIRECTLY OVER A CRAWL
SPACE NOT INTENDED FOR STORAGE OR FUEL-FIRED APPLIANCES.
(III) A PORTION OF A FLOOR ASSEMBLY WHICH COMPLIES
WITH ALL OF THE FOLLOWING:
(A) THE AGGREGATE AREA OF THE UNPROTECTED
PORTIONS SHALL NOT EXCEED 80 SQUARE FEET PER STORY.
(B) FIRE BLOCKING IN ACCORDANCE WITH SECTION
R302.11.1 SHALL BE INSTALLED ALONG THE PERIMETER OF
THE UNPROTECTED PORTION TO SEPARATE THE UNPROTECTED
PORTION FROM THE REMAINDER OF THE FLOOR ASSEMBLY.
(IV) A WOOD FLOOR ASSEMBLY USING DIMENSION LUMBER OR
STRUCTURAL COMPOSITE LUMBER EQUAL TO OR GREATER THAN TWOINCH
BY TEN-INCH NOMINAL DIMENSION OR A FLOOR ASSEMBLY
APPROVED BY A MUNICIPAL CODE OFFICIAL DEMONSTRATING
EQUIVALENT FIRE PERFORMANCE.
(I) WALL BRACING REQUIREMENTS.--SECTION R602.10 THROUGH
SECTION R602.12.1.6 OF THE 2009 INTERNATIONAL RESIDENTIAL CODE,
OR ITS SUCCESSOR PROVISIONS, ARE EXCLUDED FROM THE UNIFORM
CONSTRUCTION CODE. THE WALL BRACING REQUIREMENTS OF SECTIONS
R602.10 THROUGH R602.11.3 OF THE 2006 INTERNATIONAL RESIDENTIAL
CODE SHALL BE PART OF THE UNIFORM CONSTRUCTION CODE.
SECTION 4. RETROACTIVITY IS AS FOLLOWS:
(1) THE ADDITION OF SECTION 901(F) OF THE ACT SHALL
APPLY RETROACTIVELY TO JANUARY 1, 2010.
(2) THE ADDITION OF SECTION 901(G) OF THE ACT SHALL
APPLY RETROACTIVELY TO JANUARY 1, 2011.
Section 2 5. This act shall take effect AS FOLLOWS:
(1) THE AMENDMENT OF SECTION 107©(2) OF THE ACT SHALL
TAKE EFFECT JULY 1, 2012.
(2) THE REMAINDER OF THIS ACT SHALL TAKE EFFECT
immediately.
20110HB0377PN1520