I'm scratching my head over this BC Building Code tribunal decision.
"The brewhouse is considered to be a Group F, Division 3 occupancy. It has an area of 211m2 and a staff of 3 persons. The tap room is considered to be a Group A, Division 2 occupancy. It has an area of 235m2 and an occupant load in excess of 70 persons. The design includes only a series of stanchions and a removable belt as a separation between the two primary spaces."
The AHJ deemed the A2 occupancy to make the structure a part 3 building.
The appeal board overturned this decision.
Frankly, I don't grasp the logic. Even if the taproom is occasional use, the 70 person occupant load (combined with the alcohol consumption) make it a slam-dunk Part 3.... in my mind.
Our office dealt with a remarkably similar situation where a brewpub was proposed as a new tenancy in an existing Part 9, D-occupancy building. Both our office and the OFM deemed the new use A2, even though the actual "consumption area" wasn't as large as the brewing area and offices related to the microbrewery.
I wouldn't ask for fire separations, as one occupancy is ancillary to the other. But I would consider this a Part 3 building, with all its requirements.
BCAB 1935 – Determination of subsidiary or major occupancy
Summary of September 2024 B.C. Building Appeal Board decision.
www2.gov.bc.ca
"The brewhouse is considered to be a Group F, Division 3 occupancy. It has an area of 211m2 and a staff of 3 persons. The tap room is considered to be a Group A, Division 2 occupancy. It has an area of 235m2 and an occupant load in excess of 70 persons. The design includes only a series of stanchions and a removable belt as a separation between the two primary spaces."
The AHJ deemed the A2 occupancy to make the structure a part 3 building.
The appeal board overturned this decision.
Frankly, I don't grasp the logic. Even if the taproom is occasional use, the 70 person occupant load (combined with the alcohol consumption) make it a slam-dunk Part 3.... in my mind.
Our office dealt with a remarkably similar situation where a brewpub was proposed as a new tenancy in an existing Part 9, D-occupancy building. Both our office and the OFM deemed the new use A2, even though the actual "consumption area" wasn't as large as the brewing area and offices related to the microbrewery.
I wouldn't ask for fire separations, as one occupancy is ancillary to the other. But I would consider this a Part 3 building, with all its requirements.