Please read and comment?
210.18 Rating
Branch circuits recognized by this article shall be rated in accordance with the maximum permitted ampere rating or setting of the overcurrent device. The rating for other than individual branch circuits shall be 10, 15, 20, 30, 40, and 50 amperes. Where conductors of higher ampacity are used for any reason, the ampere rating or setting of the specified overcurrent device shall determine the circuit rating.
Exception No. 1:
Multioutlet branch circuits greater than 50 amperes shall be permitted to supply nonlighting outlet loads in locations where conditions of maintenance and supervision ensure that only qualified persons service the equipment.
Exception No. 2:
Branch circuits rated 10 amperes shall not supply receptacle outlets.
210.18 Rating
Branch circuits recognized by this article shall be rated in accordance with the maximum permitted ampere rating or setting of the overcurrent device. The rating for other than individual branch circuits shall be 10, 15, 20, 30, 40, and 50 amperes. Where conductors of higher ampacity are used for any reason, the ampere rating or setting of the specified overcurrent device shall determine the circuit rating.
Exception No. 1:
Multioutlet branch circuits greater than 50 amperes shall be permitted to supply nonlighting outlet loads in locations where conditions of maintenance and supervision ensure that only qualified persons service the equipment.
Exception No. 2:
Branch circuits rated 10 amperes shall not supply receptacle outlets.