• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Booster fans and lint traps

Badeeba

Bronze Member
Joined
Oct 22, 2009
Messages
31
I have a dental office that wants to incorporate a booster fan and lint trap (fantech) to increase the maximum distance of their dryer duct. I know these dropped out of the residential code, and were never in the mechanical code. Allowed under alternate methods and materials? Allowed under the code? Not allowed? Why? Why not?
 
Re: Booster fans and lint traps

I have yet to be given (when I asked for it) a listing for the booster fan - yes, the motors are UL listed, but no listing, or indications from a testing lab that the fans are compliant with IAPMO or IMC.
 
Re: Booster fans and lint traps

Badeeba said:
I have a dental office that wants to incorporate a booster fan and lint trap (fantech) to increase the maximum distance of their dryer duct. I know these dropped out of the residential code, and were never in the mechanical code. Allowed under alternate methods and materials? Allowed under the code? Not allowed? Why? Why not?
A test report or engineering would be a marginally reasonable requirement.

In my opinion, the booster fan is probably a better solution than a long throw dryer which may be replaced with the cheapest on sale model after a year or two of commercial use.

Relocating the dryer is an even better solution.
 
Re: Booster fans and lint traps

I am assuming that your dental office has a residential grade type of dryer and wants to

install a residential grade type of booster fan. Something to consider is the matching

of the correct [ booster ] fan to the correct type of dryer. EX: A Maytag fan to a

Maytag dryer, or a Kenmore fan to a Kenmore dryer, etc. The mixing and matching

of non-similar equipment could void the warranty, but I'm guessing that the dentist

doesn't care about all of that mumbo jumbo.

As Vegas Paul has indicated, the motors typically are not code approved. Certainly

ask for all of the documentation that you can get on the booster fans. How long of

an exhaust ducting are we talking about anyway? :?:

 
Re: Booster fans and lint traps

It is a residential dryer, the dryer run is about 60' and the booster fan is by a separate manufacturer. The installation manual for the dryer gives no mention of a booster fan as a solution. The fan is activated by a pressure switch. Also I am curious about the feasability of installing a lint trap in any condition. There is nothing in the IMC about this that I can see. If installed what are the requirements.
 
Re: Booster fans and lint traps

I do not have any personal experience with the ' lint trapped type ' of installation.

You may want to do some research via the internet to see what's out there.

Also, ask the proposed installer of the booster fan or lint trap to provide you

with as much information as you need to make a determination.

Dr. J, hearthman, and others may be able to provide some more detailed

information on this topic. Sorry, I could not help you! :(

 
Re: Booster fans and lint traps

vegas paul said:
I have yet to be given (when I asked for it) a listing for the booster fan - yes, the motors are UL listed, but no listing, or indications from a testing lab that the fans are compliant with IAPMO or IMC.
I agree with Paul. I have never found a listed booster fan assembly. Found some that said they were listed but when you looked at the paperwork only various parts were listed not the assembled appliance. No listing no use.
 
Re: Booster fans and lint traps

We have had these submitted a few times (because of a poor design for the laundry room location) and have denied their use each time. There is no provision for these units in any of the codes. None of the appliances that are available are listed for use in the USA (found one that was approved for use in Canada). I had a mechanical engineer provide calcs and upsized the ducting in lieu of the fan. The point is, with a decent design, you don't need to worry about the distance factor. Otherwise, they can get a ductless dryer that reduces the moisture to condensate that drains into the washer box. Trying to come up with solutions to problems created by poor design is working backwards. Correct the design and your problems go away.

Have the dentist provide a COMMERCIAL appliance that is factory listed for a longer duct........or he can send his laundry out.

Sometimes you just can't get there from here..........
 
Re: Booster fans and lint traps

The Commentary to the 2006 IMC (oh-oh theres that word again) alludes to the fact that dryer exhaust may be vented into a shaft that leads directly tot he outside and also indicates that the vent in the shaft must be interconnected in such a way as to prevent the dryer from working unless the exhaust fan in the shaft is activated and providing contiusous air flow through the shaft. Section 504.2.
 