1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Bracing a stud that has been cut too much

Discussion in 'Residential Building Codes' started by calf85, Mar 2, 2020.

  1. calf85

    calf85 Registered User

    Joined:
    Mar 2, 2020
    Messages:
    3
    Likes Received:
    0
    I'm installing a bathroom above an existing one, and when running the shower drain pipe I got overzealous without thinking and cut a 3" hole in a 2x4 for the drain (red circle in photo). Only 2 3/8" is allowed by code. How do I brace this to pass inspection? I was thinking about putting 2x8 blocking above and below the cut and then running king studs (with the 4" side facing out) down to the sill plate. Previous builder did something similar (yellow circle). Is that sufficient? This is old construction with 2" actual studs, plus it's at an angle, so I can't just use a stud shoe. Thoughts?

    [​IMG]
     
  2. ICE

    ICE Moderator

    Joined:
    Jun 23, 2011
    Messages:
    8,794
    Likes Received:
    1,053
    Looks like there's more studs than would be required. If you're concerned, a 16 gauge strap could make a difference.
     
  3. calf85

    calf85 Registered User

    Joined:
    Mar 2, 2020
    Messages:
    3
    Likes Received:
    0
  4. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    17,566
    Likes Received:
    1,185
    Welcome,,,

    One reason I do not do much DYI on my house, plus, I have a contractor/handyman on speed dial!!!

    Keep on going, I like the answer above, not my area, but appears enough support, but would reinforce in some manner.
     
  5. mtlogcabin

    mtlogcabin Registered User

    Joined:
    Oct 17, 2009
    Messages:
    7,598
    Likes Received:
    961
    [​IMG]
    simpson stud shoe
     
  6. calf85

    calf85 Registered User

    Joined:
    Mar 2, 2020
    Messages:
    3
    Likes Received:
    0
    I can’t use a stud shoe because the studs are too wide (2” actual) and the hole is at an angle.
     
  7. ADAguy

    ADAguy Registered User

    Joined:
    Sep 11, 2013
    Messages:
    4,390
    Likes Received:
    419
    So, get a sheet metal shop to fab one?!
     
  8. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    3,241
    Likes Received:
    465
    Do you know if the wall is load bearing?

    Simpson makes a SS2.5 which is wider and you can maybe get a spacer cut to fill the gap.

    I think the CTS-18 strap you posted if non-load bearing is better than nothing.
     
    jar546 likes this.
  9. mark handler

    mark handler Sawhorse

    Joined:
    Oct 25, 2009
    Messages:
    10,601
    Likes Received:
    871
  10. Inspector Gadget

    Inspector Gadget Registered User

    Joined:
    Mar 5, 2020
    Messages:
    5
    Likes Received:
    0
    Fascinating. Our office just put out a bulletin about professional plumbers doing exactly this. What I've allowed for, as repairs to a damaged load-bearing stud (I presume this is a load-bearing stud?) is to have a 2x4 inserted sideways to sister against the damaged member.
     