chris kennedy said:
I'll try 250.122(B) for $400 please Alex.
You would be correct, next category please.
Bryan Holland said:
Also don't forget to consider Section 300.9 of the 2008 NEC...
Yes, this section would also be applicable unless you terminated the NM cable at the required disconnecting means at the building wall and transitioned to a suitable wiring method to the unit itself.
globe trekker said:
Since this teaser question is for a residence, the NEC will not apply ( in most jurisdictions ). TheIRC is the governing code... yes?
I will give you the IRC sections.
Chris K.,Article 250.122(B) ( in the `08 NEC ) is for the sizing of equipment grounding conductors. Is
this what you intended?
Yes, the section that he post is correct.
IRC Section E3908.12 (2009 IRC) last sentence before the Table states;
"Where ungrounded conductors are increased in size, equipment grounding conductors shall be increased proportionally according to the circular mil area of the ungrounded conductors."
In my example the ungrounded conductors have been increased in size therefore the equipment grounding conductor must be increased proportionally.
For a 30 amp overcurrent device the EGC is required to be a #10 the same size as the ungrounded conductors. So if I increase the ungrounded conductors to a #8 the EGC must also be a #8. 8/2 NM cable has a #10 EGC therefore it is a violation. (Albeit a very minor one in my opinion in this instance)
Bryan,Your Article 300.9 in the NEC would correspond to Table E3701.4, "allowable applications", the
column for NM.
.
Also 2009 IRC Section E3802.7 Mirrors section 300.9 in the NEC.
Chris