2009 IMC 505 says domestic stoves only in dwelling units need exhaust. Doesn't a domestic stove in a B use break room need exhaust?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Jump over to 507.2.3 Domestic Cooking Appliances used for commercial purposesRick18071 said:2009 IMC 505 says domestic stoves only in dwelling units need exhaust. Doesn't a domestic stove in a B use break room need exhaust?
There is a difference between Domestic cooking appliances used in commercial buildings and Domestic cooking appliances used for commercial purposes.Gregg Harris said:Jump over to 507.2.3 Domestic Cooking Appliances used for commercial purposes
I like that code section " that is just dumb"mark handler said:When in doubt....go to the definitions....COMMERCIAL COOKING APPLIANCES. not Residential Appliances used in a commercial building
You guys are blowing this thing why out of proportion.
What is the hazard?
I have Never in the almost thirty years of dealing with codes and building departments has any building or fire official required a Type l or type ll hood in a office break room, that is just dumb.
I agree completely on both counts Mark, I was only pointing out what is writtenmark handler said:There is a difference between Domestic cooking appliances used in commercial buildings and Domestic cooking appliances used for commercial purposes.These guys have nicely defined it
https://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=2&cad=rja&ved=0CDUQFjAB&url=https%3A%2F%2Fwww.sanantonio.gov%2Fsafd%2FFPForms%2FCI2008006.pdf&ei=xS0pUqvqHqi2igLdwYGADQ&usg=AFQjCNGSZ_Hf-kqzLzFMwM5aVcUs50H4Fw&sig2=Gz6QJhXjmSjfQo1P034crA&bvm=bv.51773540,d.cGE
Yes in my opinion you need an exhaust. but not a type I or type II hood
The code is not dumb, it is how it has been interpretedcda said:I like that code section " that is just dumb"
commercial food service establishmentsteveray said:There is no interpretation Mark...COMMERCIAL COOKING APPLIANCES. Appliances used in a commercial food service establishment
For the purpose of this definition, a food service establishment shall include any building or a portion thereof used for the preparation and serving of food
It doesn't say for sale or for public consumption or any way to quantify it at all....I may not agree with it, I may even think it is dumb, but until someone changes the sections.....
You are assuming the microwave will not heat or cook food and which produce grease vapors, steam, fumes, smoke or odors ....peach said:When in doubt.. install a microwave instead.
Some of us, do not have a problem now.....Rick18071 said:If they just took out "dwelling units" out of this section there would not be a probem.
As you posted "... does not need a type 1 or type 2 system...."Rick18071 said:Just found it in the commentary under IMC 505. Domestic stoves that are made for dwelling units but being used in commercial buildings but not for commercial use does not need a type 1 or type 2 system. This code section is really written bad. It should not say only in "dwelling units".
Which code? IMC? UMC?BSSTG said:Greetings,I want to know how we are requiring domestic use ovens to have exhaust hoods out of this section 505 no matter where they are used? Looks to me like the section is dealing specifically with downdraft exhaust.
SECTION 505 DOMESTIC KITCHEN EXHAUST EQUIPMENT
505.1 Domestic systems. Where domestic range hoods and domestic appliances equipped with downdraft exhaust are located within dwelling units, such hoods and appliances shall discharge to the outdoors through sheet metal ducts constructed of galvanized steel, stainless steel, aluminum or copper. Such ducts shall have smooth inner walls and shall be air tight and equipped with a backdraft damper.
BSSTG
2003 IMCmark handler said:Which code? IMC? UMC?What year?