Condition is main 200A panel with 6 awg feeder to supply a sub-panel what size breaker allow to use? Assuming ambient 45 C, THHN, GC argue for 70A but I
said it only allow for 60A.
My argument from 110.14.C The temperature rating of conductor not to exceed the lowest temperature rating of any connected termination. Most of the breaker ambient rating are 40 C, and 60/75 C wire. Am I right or wrong?