My take on 509
509 exempts or modifies the allowable height and area based on occupancy and construction types
509.1 General.
The provisions in this section shall permit the use of special conditions that are exempt from, or modify, the specific requirements of this chapter regarding the allowable heights and areas of buildings based on the occupancy classification and type of construction, provided the special condition complies with the provisions specified in this section for such condition and other applicable requirements of this code.
509.2 requires all 5 requirements to be met
509.2 Group S-2 enclosed or open parking garage with Group A, B, M, R or S above.
A basement and/or the first story above grade plane of a building shall be considered as a separate and distinct building for the purpose of determining area limitations, continuity of fire walls, limitation of number of stories and type of construction when all of the following conditions are met:
Requirement #4 is the building below the horizontal assembly be a Group S-2 parking garage
4. The building below the horizontal assembly is a Group S-2 enclosed or open parking garage, used for the parking and storage of private motor vehicles.
Exception #2 provides for additional limited Occupancy Groups if protected by an approved automatic sprinkler system.
Exceptions:
2. Multiple Group A uses, each with an occupant load of less than 300, or Group B or M uses shall be permitted, in addition to those uses incidental to the operation of the building (including storage areas), provided that the entire structure below the horizontal assembly is protected throughout by an approved automatic sprinkler system.