Hello everyone, longtime reader first time poster. Usually I can navigate the Code pretty well, but this one is tricky.
Here's my situation. I have a 4-unit townhouse development, adaptive re-use building on top of 4 single-level business occupancies. The existing lower level of each unit will become the lower level of the each new 2-storey townhouse. These are separate parcels, now under single ownership. The units are very small, 400-700 square feet per floor. Trust me, I would rather tear it down and start from scratch, but there are local reasons for going this route (boutique town, grandfathered footprint).
Townhouses would require 2-hr separation, with independent structure on each side. Tough to do this over the existing first floor walls. We also have to protect openings 4' on either side of the fire walls between units, same for the roof, etc. Because these units are so small, this is limiting.
If I call it R2, we have to sprinkler the whole "building" but can use NFPA 13R, so it's not a deal breaker. And my separation goes to 1-hour, with no independent structure required because I'm now building Fire Partitions between units. And opening protection either side of the fire partitions is not required. Same for the roof.
I guess the question is, can I classify this as an R2 building? And is there anything else I'm missing? Assuming the parcels would have to be re-combined into a single parcel.
Thanks
Jesse
Here's my situation. I have a 4-unit townhouse development, adaptive re-use building on top of 4 single-level business occupancies. The existing lower level of each unit will become the lower level of the each new 2-storey townhouse. These are separate parcels, now under single ownership. The units are very small, 400-700 square feet per floor. Trust me, I would rather tear it down and start from scratch, but there are local reasons for going this route (boutique town, grandfathered footprint).
Townhouses would require 2-hr separation, with independent structure on each side. Tough to do this over the existing first floor walls. We also have to protect openings 4' on either side of the fire walls between units, same for the roof, etc. Because these units are so small, this is limiting.
If I call it R2, we have to sprinkler the whole "building" but can use NFPA 13R, so it's not a deal breaker. And my separation goes to 1-hour, with no independent structure required because I'm now building Fire Partitions between units. And opening protection either side of the fire partitions is not required. Same for the roof.
I guess the question is, can I classify this as an R2 building? And is there anything else I'm missing? Assuming the parcels would have to be re-combined into a single parcel.
Thanks
Jesse