Your assumption is incorrect.codewonk said:Do the span tables in chapter 5 of the IRC for girders and headers (built up headers) correlate directly to dimensioned headers of the same size? I assume they do but I can't find the exact reference which states so.
Well, sure. You already know my stance on the wordage of 'design professional' vs. 'registered design professional'.brudgers said:That's why I recommended a design professional.
It is best for either class of person to simply write on the plans that the girder meets the code requirements. If the AHJ wants to do the math, he/she can.RickAstoria said:Unlicensed persons would most likely need to ...Registered Engineers can just ...
And you know mine.RickAstoria said:Well, sure. You already know my stance on the wordage of 'design professional' vs. 'registered design professional'..
Codewonk:Paul Sweet said:As GHRoberts and Brudgers pointed out, you can't substitute directly because timbers have lower strengths than 2-bys. For instance, #2 Southern Yellow Pine has a bending strength of 1200 PSI for a 2x8, 975 PSI for a 2x12, and only 850 PSi for a timber ( http://www.southernpine.com/designvalues.shtml )I like to use the Western Wood Products Association Span Calculator to size joists & beams. http://www.wwpa.org/store/product1.asp?SID=3&Product_ID=13
I didn't misunderstand your post.RickAstoria said:Design values does have some factor of safety built-in for the relatively statistical variability of one grade lumber from another of same grade.
Brudgers: you misunderstood my post earlier. The bottom line: it needs to be properly calculated and cross-section of built-up beam means more then ply thickness. Depending on state laws, an unlicensed person may perform the calcs but must be done correctly and the math must be shown to show how you arrived to the specifications such as beam dimensions and spans. So an unlicensed person would need to do the math the old-fashion way.
Design values does have some factor of safety built-in for the relatively statistical variability of one grade lumber from another of same grade.brudgers said:I didn't misunderstand your post.It was perfectly clear that you were offering the sort of bad advice that requires the very licensing laws you dismiss.
And continue doing so, as I highlighted.
I suggest you look at the reference design values for DF-L timbers in the NDS supplement http://www.awc.org/pdf/2005-NDS-Supplement.pdf . While dense select structrural timbers may be impractical (cost and availablitlity), the grading rules and design properties are published.RickAstoria said:Solid-hewn timber grading never exceeds what would in lumber grading #1 / #2 grade because grains can not be consistant throughout entire cross-section.
Price and availability rather than strength make built-up beams attractive.RickAstoria said:Built-Up beams can be built stronger then a solid-hewn lumber even if actual dimensions are slightly smaller because you can be more controlled on the lumber.
Glulams are a good alternative to timbers when the appearance of the timber is not as important. Glulam, Glu-Lam, GLB are all short for Glue-Laminated Beams (also used for posts). Glulams should not be confused with PSL, LVL or other engineered lumber. People will be confused if the term glulam is used for site constructed built-up members. Glulams have stress rating and combinations with published design values similar to dimensional lumber.RickAstoria said:Glu-lam is even stronger yet. (Glu-Lam is the term for any pre-manufactured and engineered beam. Field-built glu-laminated beams are called "Built-Up beams" as well as ones nailed together. Including combination nailed and glued.
Until it falls on your head because a building designer decided to reduce the factor of safety.peach said:Once you're out of the cookbook (prescriptive) provisions of the code.. you are into an engineered structural design. Not that hard.