bulkhead too low?
Nicole Brooks
Baltimore
I'm working on an existing building. Current floor to floor is 8'7", I have approximately 7'-7" clear. I have an enclosed bulkhead that has an 8" duct, with approximately 1.5" for connections (so 9.5") and it is enclosed with 2 1/2" studs. So, with drywall that puts me just over 6'-8" clear. the bulkhead is 3.5' wide and cuts across (perpendicular) my exit access corridor. Does a bulkhead fall under exception 1003.3.1: Protruding objects are permitted to extend below the min. ceiling height required by section 1003.2 where a min. headroom of 80" is provided over any circulation path, cooridors, aisles and passageways. Not more than 50% of the ceiling in a means of egress shall be reduced in height by protruding objects.
Gotta love regional terminology. Around here, a "bulkhead" is a structure above the roof level of a building, like an elevator penthouse or a rooftop mechanical room.
I don't see anything confusing about IBC section 1003.3 or 1003.3.1.
Your protruding construction provides 80" if headroom -- check.
The protrusion is 3-1/2 feet wide. What's the width of the corridor and what's the length of the corridor? If the horizontal projection of the protruding duct enclosure is not more than 50% of the ceiling area of the corridor, you're in compliance.
The corridor is 36' long and 9' wide
Assuming uniform corridor width, the protrusion is 3.5' long and the corridor is 36' long. That's 9.7%, which is considerably less than 50%.
I have heard and maybe used it for a duct below ceiling and against wall - a kind of soffit.
From Merriam Webster
1: an upright partition separating compartments
2: a structure or partition to resist pressure or to shut off water, fire, or gas
3: a retaining wall along a waterfront
4: a projecting framework with a sloping door giving access to a cellar stairway or a shaft
If you’re concerned and want a little cushion on the headroom, convert the 8” round duct to a 3” or 4” h x whatever width rectangle.
LOL it was new to me too when I moved to the mid-Atlantic, would have referred to it as a soffit before.
A soft is the build out above the kitchen cabinets, or the space under the roof overhang, or the boxing out of the mechanical at the permitter of the room
Does "underside" as used here imply level? I noted "stair" and it never occured the boxed in sloped part under a stair was a bulkhead.
Assuming spell correct are your "soffit", would the build out still be a soffit if there were no cabinets?
Sssspell check at work, Soffit lacking a cabinets I would still call it a soffit
How about a reception desk in a doctors' office waiting room? We're seeing a lot of medical offices in which the general waiting room has an acoustical tile (lay-in) ceiling at, say, 9 feet AFF, and above the reception desk there's a dropped section of sheetrock ceiling at 8 feet AFF. It's in the middle of the room, not along any wall. We call that a soffit.