Ca code section please
The correction was written by an inspector. I have not seen such a placard. I can understand the 4x4 placard on the table but the 25x30 on the floor seems out of line. Is this a thing?
Does he want a dashed line on the floor like you see on the permit drawings? Maybe a dashed-line circle in the restrooms …
I am not even sure what a 2?x30 clear space is supposed to provide at the (assumed?) dining surface, marked or not.
Realized after that they may just want a squarish ISA on the floor to designate the seating as accessible, but I've never seen anyone require it.
2019 CBC 11B-221 Assembly Areas
11B-221.1 General
Assembly areas shall provide wheelchair spaces, companion seats, designated aisle seats and semi-ambulant seats complying with Sections 11B-221 and 11B-802. In addition, lawn seating shall comply with Section 11B-221.5.
11B-221.2 Wheelchair Spaces
Wheelchair spaces complying with Section 11B-221.2 shall be provided in assembly areas with fixed seating.
Note: When required wheelchair spaces are not occupied by persons eligible for those spaces, individual, removable seats may be placed in those spaces.
11B-221.2.1 Number and Location
Wheelchair spaces shall be provided complying with Section 11B-221.2.1.
  • Like
Reactions: ICE
11B-221.1 General
Mark, I think his question is: where is the 4"x4" ISA symbol "permanent placard" required by code?
In the sections you quoted above, the only place I see "identification" signage is in 802.4.2 for "designated aisle seats"
Maybe it’s common sense … to keep the restaurant staff from placing a chair there, and to make it obvious that the restaurant has a dedicated HC space.
How do you "designate" (per Code) something without identifying it to the end users and "regulators". You can callout all kinds of stuff on the plans, how is the guy/girl making $8 bucks an hour going to know that?
The original post was not about the operators of the facility. It was about a building inspector writing a "correction" for which there is no code citation to indicate a violation.
How does a building inspector say this is a "correction", when there is no code violation?
Show How you "designate" the space.
Code does not say to whom, therefore, designate to all.
Show How you "designate" the space to others.
Really poor image, but all I could find. This is typical to what I have seen. Small, 2"x2" label showing designated accessible seating.
I will say, this is great, but not required. Accessible seating can be provided/accommodated by simply removing a chair from a table (34" height).
That happens a lot more than people know. I have hundreds of examples.
In my opinion, you "designate" it on the plans, analogous to how you show 60" turning circle on the plans to demonstrate to the plan checker that you have provided enough designated space for wheelchair maneuvering.
Also, please note that the word "designate" in 11B-221.1 is specifically referring ONLY to "designated aisle seats". I already mentioned in post #6 that this is the only one that refers to 802.4.2.
Notice that 703.7.2.1 does not mention any specific required dimension:
I don't know of a IBC or ANSI 117.1 section that requires ISA on an accessible seating space at a table. The biggest problem I have with accessible tables is they use tables that have a center column all the time which does not allow for the toe space because of the large round base or X base. Just wondering if others fail accessibility inspections because of this because I do every time when an accessible seating space is required.
In San Diego that is reviewed during plan check and sometimes at final.
We would do the same. At plan check, if the tables show a center column (we all know they don't always show that), I make them detail the accessible one with at least a plan view showing how it will meet the minimum clear requirements.
As suggested by many, identification of accessible seating areas is not required unless it is a designated aisle seat.
For the typical restaurant dining area, it is not required that signage or other marking be provided to indicate accessible use. If signage were required, it would be found in IBC Section 1111.1 (below).
1111.1 Signs
Required accessible elements shall be identified by the International Symbol of Accessibility at the following locations.
  1. Accessible parking spaces required by Section 1106.1.
    Exception: Where the total number of parking spaces provided is four or less, identification of accessible parking spaces is not required.
  2. Accessible parking spaces required by Section 1106.2.
    Exception: In Group I-1, R-2, R-3 and R-4 facilities, where parking spaces are assigned to specific dwelling units or sleeping units, identification of accessible parking spaces is not required.
  3. Accessible passenger loading zones.
  4. Accessible rooms where multiple single-user toilet or bathing rooms are clustered at a single location.
  5. Accessible entrances where not all entrances are accessible.
  6. Accessible check-out aisles where not all aisles are accessible. The sign, where provided, shall be above the check-out aisle in the same location as the checkout aisle number or type of check-out identification.
  7. Family or assisted-use toilet and bathing rooms.
  8. Accessible dressing, fitting and locker rooms where not all such rooms are accessible.
  9. Accessible areas of refuge in accordance with Section 1009.9.
  10. Exterior areas for assisted rescue in accordance with Section 1009.9.
  11. In recreational facilities, lockers that are required to be accessible in accordance with Section 1109.9.
  • Like
Reactions: ICE
I almost never see furniture on plans. And if they did they don’t show what kind of legs they have.
I have made a couple restaurants replace the minimum number of center column tables with four leg tables to comply but if I stop by after the CO The center column tables are back.