• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

Cables for Machine Room-less Elevator

Paul Sweet

SAWHORSE
Joined
Oct 17, 2009
Messages
2,798
Location
Bedford, VA
We just had a new machine room-less elevator fail inspection because it had seven 8 mm cables, instead of the three or more 9.5 mm cables required by ASME A17.1-2005 2.20.4. The specs. called for cables to be at least 10 mm, but the A/E missed that when reviewing the shop drawings.

We need to request a code modification allowing the smaller cables. Does anyone know if there are pending amendments to ASME A17.1 that allow the smaller cables, as long as there are more of them? If not, has anyone else had to request a code modification, and how did you justify the request?
 
Re: Cables for Machine Room-less Elevator

elevators are a delicate balance...

the design professional needs to prove that as installed, it meets the intent..

dropping 10 or more floors in an elevator.. to my death.. is not top on my list of ways to go.
 
Re: Cables for Machine Room-less Elevator

I would rely heavily on the manufacturer. The machine room less units are newer and do not have the extensive track record as do conventional traction or hydraulic.
 
Re: Cables for Machine Room-less Elevator

Paul,

I agree with peach and Coug Dad. I would contact the manufacturer and discuss options. Also, a certified

elevator installer is required to furnish a certifcate that the elevator(s) were installed according to the

manufacturer' specs.

As peach has stated, elevators ARE a delicate balance. They have a bunch of requirements. What is

the number of stories n your application?

.
 
Re: Cables for Machine Room-less Elevator

MRL elevators are becoming more and more common.. they are smooth riding and stop where they should... but you need to look at what the manufacturer requires and the ASME 17.1 that covers them.. it's a new(er) product. If you are under an older code, it's actually a modification to allow them.
 
Re: Cables for Machine Room-less ElevatorI submitted a code modification request, based on calculations showing that the steel wire ropes that were used have a factor of safety of 21, which is far more than the elevator code requires, and on proposed changes to the 2010 elevator code to allow smaller steel wire ropes, aramid fiber ropes, and steel reinforced belts.This elevator and the building are both interesting. The building is a college library on the side of a hill in Southwest Virginia, and has some incredible brick sculptures inside. You enter the building o the upper level, which is at the top of the hill, go downstairs, out of the building and across a short bridge, down this elevator about 30 feet, then across another short bridge to the roof of the building below.View from NE 9-19-09.jpg[/attachment:2hbvzvl1]

View attachment 47

View attachment 47

/monthly_2010_05/572953b4321f7_ViewfromNE9-19-09.jpg.07d4858164a37188df6964dc14c6729e.jpg
 
Back
Top