1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

CAL GREEN - Exterior Door Protection

Discussion in 'Green / Leed' started by RANDOM, Jul 11, 2016.

  1. RANDOM

    RANDOM Member

    Joined:
    Apr 11, 2016
    Messages:
    49
    Likes Received:
    5
    CAL GREEN
    Section 5.407
    Water Resistance & Moisture Management

    5.407.2.2.1 Exterior Door Protection.

    Primary exterior entries shall be covered to prevent water intrusion by using a non absorbent floor and wall finishes within at least 2 feet around and perpendicular to such opening.

    Does the floor width need to span more than the actual width of the door?

    For what I can tell, I would draw the door and offset a line 2 feet away in both directions (x,y)

    Any feedback?
     
  2. mark handler

    mark handler Sawhorse

    Joined:
    Oct 25, 2009
    Messages:
    10,515
    Likes Received:
    835
    Guide to the 2013 California Green Building Standards Code (Nonresidential)
    http://www.documents.dgs.ca.gov/bsc/CALGreen/CALGreen-Guide-2013-FINAL.pdf

    The intent of this code provision is to minimize the amount of moisture entering the building; at the exterior entries and openings from wind-driven rain and at exterior walls from poorly designed sprinkler systems.

    For entries and openings:
    1. Specify nonabsorbent flooring material at the interior landing surface a minimum of 2 feet in the direction of travel and at wall finishes adjacent to the door opening on the sides and at the top. If 2 feet is not available above the opening, wall finishes may terminate at the ceiling,
    2. Show compliance with one of the four listed requirements above, and
    3. Install flashings integrated with a drainage plane.
     
    RANDOM likes this.
  3. RANDOM

    RANDOM Member

    Joined:
    Apr 11, 2016
    Messages:
    49
    Likes Received:
    5
    Thank you Mark.
     
  4. ICE

    ICE Moderator

    Joined:
    Jun 23, 2011
    Messages:
    8,698
    Likes Received:
    1,013
    5.407.2.2.1 Exterior door protection. Primary exterior
    entries shall be covered to prevent water intrusion by
    using nonabsorbent floor and wall finishes within at least
    2 feet around and perpendicular to such openings plus at
    least one of the following:
    1. An installed awning at least 4 feet in depth.
    2. The door is protected by a roof overhang at least 4
    feet in depth.
    3. The door is recessed at least 4 feet.
    4. Other methods which provide equivalent protection.

    Live and learn, I don't pay much attention to the green code
     