Gregg Harris
Notes "b' 'c' and "g' make the kitchen, bathrooms. and closet excluded or "prohibited" from being circulated.
If you have a kitchen with no supply openings (and no return openings as per your IMC reference) and it has closed doors from the rest of the dwelling unit, I could see omitting from the ventilated volume of the rest of the dwelling unit. [Except that as a living space, the kitchen also requires 0.35 ACH, so you'd need a separate system for the kitchen.] But if it has a supply opening, the air will be mixed with the rest of the dwelling unit, since all of that supply air must make it to the return openings (or rather, an equivalent volume of air).IMC 601.5(7) Should prevent the air from being "well mixed,"
If you have a single air system for a dwelling unit subject to IMC 403.3.1, seems like those notes just mean you can't put a return air opening in the kitchen or bathrooms (which matches IMC 601.5(7)). If you have a supply opening in one of those rooms, its air will be mixed with the rest of the dwelling unit as the air returns to some return opening.Notes "b' 'c' and "g' make the kitchen, bathrooms. and closet excluded or "prohibited" from being circulated.
Where in the code does it specify that the kitchen is considered part of the living space?If you have a kitchen with no supply openings (and no return openings as per your IMC reference) and it has closed doors from the rest of the dwelling unit, I could see omitting from the ventilated volume of the rest of the dwelling unit. [Except that as a living space, the kitchen also requires 0.35 ACH, so you'd need a separate system for the kitchen.] But if it has a supply opening, the air will be mixed with the rest of the dwelling unit, since all of that supply air must make it to the return openings (or rather, an equivalent volume of air).
Cheers, Wayne
The definition of living space in Chapter 2 of the IMC: "Space within a dwelling unit utilized for living, sleeping, eating, cooking, bathing, washing and sanitation purposes."Where in the code does it specify that the kitchen is considered part of the living space?
That table uses the term "living areas" for some reason, which is not defined in Chapter 2, but it appears to be synonymous with "living spaces".Where in the table 403.3.1.1 does it say that 0.35 ACH is required in the kitchen?
Cheers, Wayne
I don't see that definition in the IMC. And Table 403.3.1.1 doesn't use the term "habitable space." So I'm not seeing the relevance.Habitable space
A space in a building for living, sleeping, eating or cooking. Bathrooms, toilet rooms, closets, halls, storage or utility spaces and similar areas are not considered habitable spaces .
Cheers, Way