Existing concrete apartment building in Los Angeles is receiving a new heat pump system (ductless mini-splits), with new condensers up on the roof.
Previously, the only HVAC system in the apartments was radiant steam heat, and a bath exhaust fan.
The mechanical engineer says CA code will require fresh air supply for Indoor Air Quality at the existing apartments. In the past we've done a low-speed continuous bath exhaust fan (switches to high speed via occupancy sensor), and the front door of the unit would have a 1/2" undercut for fresh air supply from the corridor.
When I shared this with the engineer, they replied: "The front door undercut does not accept fresh air intake; you can only use it for bathrooms. You need to provide outside air with a supply fan."
Q: Do you know of anything in the codes that prohibits use of a door undercut to supply whole house IAQ, especially on an existing building?
Previously, the only HVAC system in the apartments was radiant steam heat, and a bath exhaust fan.
The mechanical engineer says CA code will require fresh air supply for Indoor Air Quality at the existing apartments. In the past we've done a low-speed continuous bath exhaust fan (switches to high speed via occupancy sensor), and the front door of the unit would have a 1/2" undercut for fresh air supply from the corridor.