In California, per Green Code mandatory residential requirement 4.503, fireplaces must be "direct-vent sealed-combustion type".
Plan checker noted the above requirements (without code section) and then also noted:
Manufacturer's literature requires just 1'-0" for Flat to 6/12 roof. I can add the instruction page to the drawings along with fireplace spec sheet.
Do I have this correct?
Plan checker noted the above requirements (without code section) and then also noted:
- Chimney vents shall terminate at least 2 ft above any point on the roof within 10 ft horizontally of the vent. CMC 802.5.4
- Chimney vents shall extend a minimum of 3 ft above the highest point of the vent penetration. CMC 802.5.4
802.2.6 Direct Vent Appliances. Listed direct vent appliances shall be installed in accordance with the manufacturer's installation instructions and Section 802.8.2. [NFPA 54:12.3.5]
The code plan checker references is for 802.5 Masonry, Metal, and Factory-Built Chimneys.Manufacturer's literature requires just 1'-0" for Flat to 6/12 roof. I can add the instruction page to the drawings along with fireplace spec sheet.
Do I have this correct?