Can a Furnace Closet Serve as a Return Plenum? Here’s What the Code Actually Says
A recent clarification from the ICC sheds light on a recurring field question: Can a closet housing a direct-vent furnace be used as a return air plenum? According to the interpretation, yes, but only under very specific conditions.
Section 618.4 of the 2015 International Fuel Gas Code (IFGC), specifically Exception 1 to Item 5, permits this type of arrangement only when the furnace is a direct-vent appliance. That’s because a direct-vent unit brings in combustion air from the exterior and vents flue gases directly outdoors, eliminating the risk of drawing contaminants from the indoor air. This exemption continues to apply in the 2018, 2021, and 2024 editions of the IFGC.
However, the story doesn’t stop there. Just because the IFGC allows it doesn’t mean the installation is automatically code-compliant.
The International Mechanical Code (IMC) plays a significant role in regulating plenums. Per Section 602.2 of the 2015 IMC, any space used as a plenum must meet strict construction standards. That includes complying with Section 202's definition of a plenum and addressing several specific code sections, such as:
  • 602.2.1.1: Electrical wiring in plenums
  • 602.2.5: Installation of discrete plumbing and mechanical items
  • 602.2.7: Use of plastic piping
These provisions apply because the closet is no longer just a storage or equipment space—it’s now functioning as part of the return air system, which brings with it a higher standard of fire and smoke safety.
To add another layer, the International Energy Conservation Code (IECC), specifically Section R403.3.5 of the 2015 edition, explicitly prohibits using building framing cavities as plenums in residential buildings (one- and two-family homes, townhouses, and R-2, R-3, and R-4 occupancies up to three stories). While the IECC doesn’t define “building cavity,” the context makes clear that this includes wall, floor, and ceiling cavities not specifically built for the sole purpose of conveying air.
The bottom line: While the IFGC may allow a closet to serve as a return plenum for a direct-vent furnace, all components of the closet must comply with the IMC’s construction standards for plenums. Additionally, the plenum must not utilize structural cavities as return pathways if governed by the IECC. If the installation relies on the wall, ceiling, or floor cavity itself to move air, instead of a dedicated duct or a purpose-built plenum, it is not code-compliant.
This highlights the importance of applying all relevant codes, not just the one you're reading from. Always verify cross-code compliance before signing off on a design or approving an installation.
Not sure who made that interpretation, but they missed a couple of very relevant sections specifically prohibiting it. A furnace closet with a fuel fired furnace cannot serve as a return plenum.
The last sentence of IMC 602.1 specifically prohibits fuel fired appliances in plenums. Also, IMC 601.5 item 7 and IRC 1602.2 item 4 specifically prohibit taking return air from a furnace room. If the room is a plenum, you are taking return air from the furnace room.
Because fuel fired appliances are specifically prohibited in plenums, IFGC 618.4 would apply where the room or space is NOT a plenum, such as a furnace located in a work area or tucked in the corner of a retail space. At that point the furnace is located in occupiable space, not a furnace room or closet.
Technically not "from" but "through."
So which one is applicable to a one and two family dwelling? Chapter 16 or Chapter 11 of the IRC.
I allow Chapter 16 since the language in the IEEC also applies to apartment buildings and not specifically to one and two family dwellings
2021 IRC
  1. 7.Stud wall cavities and the spaces between solid floor joists to be used as air plenums shall comply with the following conditions:
    1. 7.1.These cavities or spaces shall not be used as a plenum for supply air.
    2. 7.2.These cavities or spaces shall not be part of a required fire-resistance-rated assembly.
    3. 7.3.Stud wall cavities shall not convey air from more than one floor level.
    4. 7.4.Stud wall cavities and joist-space plenums shall be isolated from adjacent concealed spaces by tight-fitting fireblocking in accordance with Section R302.11. Fireblocking materials used for isolation shall comply with Section R302.11.1.
    5. 7.5.Stud wall cavities in the outside walls of building envelope assemblies shall not be utilized as air plenums.
    6. 7.6.Building cavities used as plenums shall be sealed.
2021 IRC