redeyedfly
206.2.1 Ex. 2example of ICC not complying w/ ADASAD
Typically...not required to be marked.
2019 CA Building Code 11B-206.2.1 Site Arrival PointsDon't know CA codes but 2015 IBC has this:
Exception: Other than in buildings or facilities containing or serving type B units, an accessible route shall not be required between site arrival points and the building or facility entrance if the only means of access between them is a vehicular way not providing for pedestrian access.
If it wasn't for the exception a lot of camps back in the woods would have problems.
Can you describe an example of what you’ve required to be added? Has it involved additional paving and grading?2019 CA Building Code 11B-206.2.1 Site Arrival Points
At least one accessible route shall be provided within the site from accessible parking spaces and accessible passenger drop-off and loading zones; public streets and sidewalks; and public transportation stops to the accessible building or facility entrance they serve. Where more than one route is provided, all routes must be accessible.
- Reserved.
- An accessible route shall not be required between site arrival points and the building or facility entrance if the only means of access between them is a vehicular way not providing pedestrian access.
- General circulation paths shall be permitted when located in close proximity to an accessible route.
But, If there is a way to provide that path of travel, even though it does not currently exist, I require them to add the POT.
I can't see how you make them do that when it's clear that the exception says that it's not required. Your making up your own codes.But, If there is a way to provide that path of travel, even though it does not currently exist, I require them to add the POT.
Where?Chapter 1 of the CBC and ICC allow AHJ's to exceed code minimums.
I'm not making up anythingI can't see how you make them do that when it's clear that the exception says that it's not required. Your making up your own codes.
If it is possible, it is requiredI can't see how you make them do that when it's clear that the exception says that it's not required. Your making up your own codes.
ADAGuy, I believe that when Rick 18071 was saying "we don't enforce ADA", he meant "we, as building officials in PA, are legally allowed to plan check and enforce only the codes adopted by our jurisdiction, and ADA is not a code adopted by our jurisdiction".Enforcement of ADASAD is not based on ICC if ICC items are less than ADASAD mins.
ICC is not a warranty of ADA compliance, only code. ADA is a "law", not a code.