Michigan Building Code 2021
40,000sf type A-3 single story pre-fab structure IIB construction with Fire suppression
Doing a code review for a possible trampoline park. The main 40,000 sf portion of the building would be considered Unlimited area per section 507.6 for A-3 of IIB. Owner is wanting to add a 3,000 sf (2) story appendage to the footprint. First floor will be A-3, second floor will be A-2 party rooms.
So my problem is that the building does not fall into unlimited if there is a second story. So can I consider it an Accessory occupancy.
But my problem is understanding this part of section 508.2.3
"The allowable area of the building shall be based on the applicable provisions of section 506 for the main occupancy of the building. Aggregate accessory occupancies shall not occupy more than 10 percent of the floor area of the story in which they are located and shall not exceed the tabular values for nonsprinklered buildings.
So the accessory A-2 is on another story. Is it still considered accessory to the building A-3 if there is no other A-3 on that "story"
Or am I going to get back looped into the building area chart and not considered Unlimited because it has (2) stories.
40,000sf type A-3 single story pre-fab structure IIB construction with Fire suppression
Doing a code review for a possible trampoline park. The main 40,000 sf portion of the building would be considered Unlimited area per section 507.6 for A-3 of IIB. Owner is wanting to add a 3,000 sf (2) story appendage to the footprint. First floor will be A-3, second floor will be A-2 party rooms.
So my problem is that the building does not fall into unlimited if there is a second story. So can I consider it an Accessory occupancy.
But my problem is understanding this part of section 508.2.3
"The allowable area of the building shall be based on the applicable provisions of section 506 for the main occupancy of the building. Aggregate accessory occupancies shall not occupy more than 10 percent of the floor area of the story in which they are located and shall not exceed the tabular values for nonsprinklered buildings.
So the accessory A-2 is on another story. Is it still considered accessory to the building A-3 if there is no other A-3 on that "story"
Or am I going to get back looped into the building area chart and not considered Unlimited because it has (2) stories.