Can I simply add fire ratings ?

blugosi

SAWHORSE
Joined
Sep 25, 2018
Messages
121
Location
Greece
While protecting columns, can we simply add fire ratings achieved by different rating methods?
I mean, if we have a column with 1 hour of fire rating based on vermiculite or intumescent paint and we enclose it in gypsum boards calculated for say 1 hour, do we get a two hours fire rating on the column?
 
The prescriptive values in IBC (2021) Table 721.1(1) do not seem to allow adding/combining systems At least, the footnotes do not say that adding is allowed.

The situation is different under the IEBC -- that's why I asked what code you are under.
 
While protecting columns, can we simply add fire ratings achieved by different rating methods?
I mean, if we have a column with 1 hour of fire rating based on vermiculite or intumescent paint and we enclose it in gypsum boards calculated for say 1 hour, do we get a two hours fire rating on the column?

Generally no. You can only "build your own assembly" up to a 1 hour rating; anything higher requires a tested, listed UL assembly. Which could include a multitude of different products and approaches.

I suspect if you want a 2 hour you need to go for the two layers of Type X. Gyp is cheap, no reason to make your life harder with the building official.
 