Can you have unseparated uses nested within overall separated uses?

Ryan Schultz

SAWHORSE
Joined
Apr 2, 2012
Messages
283
Location
Madison, WI
Can you do something like the following? That is, having unseparated uses nested within overall separated uses?
For this example assume unsprinklered Type VB.

shapes at 23-12-05 14.59.52.png
 

2021 IBC 508.1 General

Each portion of a building shall be individually classified in accordance with Section 302.1. Where a building contains more than one occupancy group, the building or portion thereof shall comply with the applicable provisions of Section 508.2, 508.3, 508.4 or 508.5, or a combination of these sections.
Exceptions:

  1. Occupancies separated in accordance with Section 510.
  2. Where required by Table 415.6.5, areas of Group H-1, H-2 and H-3 occupancies shall be located in a detached building or structure.
 