1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

canopy

Discussion in 'Commercial Building Codes' started by Hyrax4978, Oct 11, 2019.

  1. Hyrax4978

    Hyrax4978 Registered User

    Joined:
    Nov 28, 2016
    Messages:
    91
    Likes Received:
    4
    Is there a requirement for canopies at egress doors? I don't see anything requiring canopies, at entry or exit doors, but i thought there was one.

    Thanks,
     
  2. Ty J.

    Ty J. Sawhorse

    Joined:
    Aug 2, 2017
    Messages:
    646
    Likes Received:
    262
    Not a Building Code based requirement that I am aware of.

    Vestibules via most energy codes.
     
  3. e hilton

    e hilton Bronze Member

    Joined:
    Jul 2, 2014
    Messages:
    460
    Likes Received:
    110
    Some cities will require shading of windows, probably includes doors. But thats for heat load, not rain.
     
  4. Yikes

    Yikes Gold Member

    Joined:
    Nov 2, 2009
    Messages:
    1,466
    Likes Received:
    172
    You don't say where the project is located. In Calfornia, the CalGreen code has this mandatory measure for nonresidential buildings:
    upload_2019-10-11_13-12-13.png

    Note that this covering applies to "primary exterior entries", not to secondary doors. Nor does it say anything about egress-only doors.

    Even if you aren't in California, you may have a non-code sustainability standard / program requirement that is similar.
     
    JPohling likes this.
  5. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    3,795
    Likes Received:
    361
    They may also be required for medical clinics & hospitals
     
  6. mark handler

    mark handler Sawhorse

    Joined:
    Oct 25, 2009
    Messages:
    10,281
    Likes Received:
    761
    IN CA Only at 11B-206.4.10 Medical care and long-term care facilities
    Weather protection by a canopy or roof overhang shall be provided at a minimum of one accessible entrance to licensed medical care and licensed long-term care facilities where the period of stay may exceed twenty-four hours. The area of weather protection shall include the passenger drop-off and loading zone complying with Section 11B-209.3 and the accessible route from the passenger loading zone to the accessible entrance it serves.
     
  7. Hyrax4978

    Hyrax4978 Registered User

    Joined:
    Nov 28, 2016
    Messages:
    91
    Likes Received:
    4
    This would be in CT. B use.
     
  8. mark handler

    mark handler Sawhorse

    Joined:
    Oct 25, 2009
    Messages:
    10,281
    Likes Received:
    761
    No requirement that I know of under the I-Codes
     
  9. Tim Mailloux

    Tim Mailloux Registered User

    Joined:
    Feb 12, 2018
    Messages:
    156
    Likes Received:
    21
    I'm also in CT, and there is no canopy requirement in the CT Building Code that I am aware of.
     
  10. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,605
    Likes Received:
    904
    Not so much if it is just a landing, but we do have this that sometimes gets "over-enforced"

    (Amd) 1011.7.2 Outdoor conditions. Outdoor stairways and outdoor approaches to stairways
    shall be designed so that water will not accumulate on walking surfaces. In other than
    occupancies in Group R-3 and occupancies in Group U that are accessory to an occupancy in
    Group R-3, treads, platforms and landings that are part of exterior stairways in climates subject
    to snow and ice shall be protected to prevent the accumulation of same.
     