is this the same wording as Florida??????
R315.2 Where required in existing dwellings. Where
a permit is required for alterations, repairs, or additions
exceeding one thousand dollars ($1,000), existing dwellings
or sleeping units that have attached garages or fuel-burning
appliances shall be provided with a carbon monoxide alarm
in accordance with Section R315.1 Carbon monoxide alarms
shall only be required in the specific dwelling unit or sleeping
unit for which the permit was obtained.
R315.3 Alarm requirements. Single– and multiplestation
carbon monoxide alarms shall be listed as complying
with the requirements of UL 2034. Carbon monoxide detectors
shall be listed as complying with the requirements of
UL 2075. Carbon monoxide alarms and carbon monoxide
detectors shall be installed in accordance with this code, the
current edition of NFPA 720 “Standard for the Installation of
Carbon Monoxide (CO) Detection and Warning Equipment”
and the manufacturer’s installation instructions. Other
carbon monoxide alarm and detection devices as recognized
in NFPA 720 are also acceptable.
Carbon monoxide alarms required by Section R315.1 and
R315.2 shall be installed in the following locations:
1. Outside of each separate dwelling unit sleeping area in
the immediate vicinity of the bedroom (s).
2. On every level of a dwelling unit including basements.
R315.1.2 Interconnection. Where more than one carbon
monoxide alarm is required to be installed within the dwelling
unit or within a sleeping unit the alarm shall be interconnected
in a manner that activation of one alarm shall activate all of the
alarms in the individual unit.
Exception:
1. Interconnection is not required in existing dwelling units
where repairs do not result in the removal of wall and
ceiling finishes, there is no access by means of attic, basement
or crawl space, and no previous method for interconnection
existed
1. If so you should be able to use the exception for interconnection
2. if the detector is not listed for outside use, which more then likely it is not, that should take care of the outside one.
cannot see an ahj requireing you to add an entry just to add a detector.
3. they do make wireless interconnected smoke alarms, not sure if they are 110 though.