You don't have to.......I have seen it used to get out of sprinklers, but not for H&A....Never tried or had someone try that...I'm trying to figure out my next course of action? Do I need to go through EBC chapter 13?
I wonder how the stairs in the exit access corridors will affect your project. Wouldn’t the portions of the corridors leading to the stairs (marked in red below) be considered dead ends from an accessibility point of view?The building is not sprinklered and is way over allowable area per current code.
I've been refining the uses for better understanding. The building was previously a high school. They've built a new high school so now they want to open up the building for more community use. Much of the building is still being used for education purposes so no change. the previous school offices are now being used as offices for the board of education. I don't consider that a change of use. The gym is still being used by the school for team practices. There will no longer be any spectator events in the gym. for that they'll use the new school building. The business use on the northern corridor is for offices for community groups. The cafeteria is being proposes as a senior center. the band room is now being used as the meeting room for the board of education.
My role in this, is the architect for the district.
I wonder how the stairs in the exit access corridors will affect your project. Wouldn’t the portions of the corridors leading to the stairs (marked in red below) be considered dead ends from an accessibility point of view?
View attachment 15667
what portion of the building is remaining an E occupancy? Is a school active teaching classes in the building?My thinking is that I can argue that per IEBC 1011.6.2 that the change of use is equal or lesser hazard category and that the building area is acceptable.
Business areas are a lesser hazard category that education. Education areas remaining are no change. It is my thinking that Areas that are now assembly A-3, were Assembly previously. My concern is that the previous assembly spaces (cafeteria, band room), were classified as E as an accessory use per IBC 303.1.3. Can those spaces still be considered an assembly use?
As far as accessibility and the stairs go, my understanding is that when multiple exits are required by code that 2 of those need to be accessible. every portion of the building has access to at least 2 accessible exits. It is permissible to have 1 exit not be accessible. Am I misunderstanding that?
if the gym or auditorium will be used by the community after school hours for rec basketball, PTO meetings or the community drama club they need to be classified as A occupancies.the blue areas are still education spaces. the gym will be used for team practices and the auditorium will still be used for school functions. (I've reclassified the board of education offices as B use)
that is not my understanding of the intended use, but it is certainly within the realm of possibility. so the question is whether or not that changes the calculus? Those spaces, although originally classified as E as an accessory use, have always been assembly spaces and therefor the hazard category per IEBC table 1011.6 does not change.if the gym or auditorium will be used by the community after school hours for rec basketball, PTO meetings or the community drama club they need to be classified as A occupancies.
have another look at table 1011.6 , A2 & A3 are a higher hazard than E.T
that is not my understanding of the intended use, but it is certainly within the realm of possibility. so the question is whether or not that changes the calculus? Those spaces, although originally classified as E as an accessory use, have always been assembly spaces and therefor the hazard category per IEBC table 1011.6 does not change.
My argument is that, even though they were called E as an accessory use, the spaces have always been assembly spaces so nothing has changes and the hazard category has not changed. nothing has changed to make the building less safe than it was before. It makes sense in my head but i don't know if it is something that a building official will agree with.have another look at table 1011.6 , A2 & A3 are a higher hazard than E.
My thinking is that I can argue that per IEBC 1011.6.2 that the change of use is equal or lesser hazard category and that the building area is acceptable.
Business areas are a lesser hazard category that education. Education areas remaining are no change. It is my thinking that Areas that are now assembly A-3, were Assembly previously. My concern is that the previous assembly spaces (cafeteria, band room), were classified as E as an accessory use per IBC 303.1.3. Can those spaces still be considered an assembly use?
As far as accessibility and the stairs go, my understanding is that when multiple exits are required by code that 2 of those need to be accessible. every portion of the building has access to at least 2 accessible exits. It is permissible to have 1 exit not be accessible. Am I misunderstanding that?