R302.1 Exterior walls.
Construction, projections, openings and penetrations of exterior walls of dwellings and accessory buildings shall comply with Table R302.1.
Exceptions:
1. Walls, projections, openings or penetrations in walls perpendicular to the line used to determine the fire separation distance .
2. Walls of dwellings and accessory structures located on the same lot .
They are not on the same lot therefore according to Table 301 openings are not permmitted within 3 ft of a lot line. Yankee is correct in that ownership is not talked about in the code but lot lines are
FIRE SEPARATION DISTANCE. The distance measured from the building face to one of the following:
1. To the closest interior lot line ; or
2. To the centerline of a street, an alley or public way; or
3. To an imaginary line between two buildings on the lot .
Construction, projections, openings and penetrations of exterior walls of dwellings and accessory buildings shall comply with Table R302.1.
Exceptions:
1. Walls, projections, openings or penetrations in walls perpendicular to the line used to determine the fire separation distance .
2. Walls of dwellings and accessory structures located on the same lot .
They are not on the same lot therefore according to Table 301 openings are not permmitted within 3 ft of a lot line. Yankee is correct in that ownership is not talked about in the code but lot lines are
FIRE SEPARATION DISTANCE. The distance measured from the building face to one of the following:
1. To the closest interior lot line ; or
2. To the centerline of a street, an alley or public way; or
3. To an imaginary line between two buildings on the lot .