Strip mall setup. 2 unoccupied units to be converted into 1. 1st unit was a check cashing facility which I would assume was a B. 2nd unit was a Curves women's center for exercise. Due to the sq footage, the occupant load by today's standards at 50 per person would be under 50. Somewhere in the 30's.
They want to convert both of these spaces into one for an office. Neither of the existing bathrooms are accessible by today's standards. 1 cannot be accessible if left the same size and the other may meet the ANSI 117.1 2003 if it is reconfigured (possibly)
The DP has chosen renovation level 2 and the IEBC.
The proposed occupant load will be under 50.
Our plan review believes that Chapter 9 would apply, the DP is challenging that opinion. After reading the beginning of Chapter 9, I am of the same opinion as our plan reviewer.
I will ask the DP for a copy of the C of O's for the 2 units and I know they will not be able to provide them. The building was originally built under the PA Fire and Panic Act of 1927, not the I-Codes. Not sure on an exact date the strip mall was built.
We would like to see both bathrooms made accessible and is would not be technically infeaseable to do so. Since this involves ADA compliance, they cannot go to a local appeals board to challenge the opinion, they must go to the State L&I Accessibility Advisory Board.
Although we feel as though their proposal to make both bathrooms unisex and try to make one of them accessible is reasonable, we do not have the authority to allow it therefore they would have to go in front of the AAB of L&I for a variance.
With all of this information in mind, would you feel as though Chapter 9 of the IEBC applies?
They have chosen the IEBC over Chapter 34, therefore they are stuck with the requirements of the IEBC.
Thanks in advance.
They want to convert both of these spaces into one for an office. Neither of the existing bathrooms are accessible by today's standards. 1 cannot be accessible if left the same size and the other may meet the ANSI 117.1 2003 if it is reconfigured (possibly)
The DP has chosen renovation level 2 and the IEBC.
The proposed occupant load will be under 50.
Our plan review believes that Chapter 9 would apply, the DP is challenging that opinion. After reading the beginning of Chapter 9, I am of the same opinion as our plan reviewer.
I will ask the DP for a copy of the C of O's for the 2 units and I know they will not be able to provide them. The building was originally built under the PA Fire and Panic Act of 1927, not the I-Codes. Not sure on an exact date the strip mall was built.
We would like to see both bathrooms made accessible and is would not be technically infeaseable to do so. Since this involves ADA compliance, they cannot go to a local appeals board to challenge the opinion, they must go to the State L&I Accessibility Advisory Board.
Although we feel as though their proposal to make both bathrooms unisex and try to make one of them accessible is reasonable, we do not have the authority to allow it therefore they would have to go in front of the AAB of L&I for a variance.
With all of this information in mind, would you feel as though Chapter 9 of the IEBC applies?
They have chosen the IEBC over Chapter 34, therefore they are stuck with the requirements of the IEBC.
Thanks in advance.