2018 IBC
Existing strip mall tenant space being renovated for a kids play area. Sprinkler heads will be relocated / added as required.
I am thinking this will be a group A-3. The party area could be stretched to A-2.
3,000 sq ft of children's play area (I am assuming similar to the play areas at McD's, Burger King, Chick-fil-a with numerous play structures and a carpet with a roadway image for kids to run / race on).
310 sf party area (I am assuming tables and chairs with carried in food. There is no kitchen or food prep area)
98 sf sensory room
Toilet rooms and janitor closet
What occupant load density should I be using for the play area? Day care is one person per 35 sq ft net, exercise room is one person per 50 sq ft gross, a pool in one person per 50 sq ft. Using day care, there would be 86 occupants and using exercise room, there would be 60 occupants.
At 7 sf net, the sensory room would have 14 people, which is probably way higher than what will be in there.
Thanks!
Existing strip mall tenant space being renovated for a kids play area. Sprinkler heads will be relocated / added as required.
I am thinking this will be a group A-3. The party area could be stretched to A-2.
3,000 sq ft of children's play area (I am assuming similar to the play areas at McD's, Burger King, Chick-fil-a with numerous play structures and a carpet with a roadway image for kids to run / race on).
310 sf party area (I am assuming tables and chairs with carried in food. There is no kitchen or food prep area)
98 sf sensory room
Toilet rooms and janitor closet
What occupant load density should I be using for the play area? Day care is one person per 35 sq ft net, exercise room is one person per 50 sq ft gross, a pool in one person per 50 sq ft. Using day care, there would be 86 occupants and using exercise room, there would be 60 occupants.
At 7 sf net, the sensory room would have 14 people, which is probably way higher than what will be in there.
Thanks!