Chipping out post-tension slabs

jar546

CBO
Joined
Oct 16, 2009
Messages
12,938
Location
Not where I really want to be
I am starting to see a lot of post-tension slabs being chipped out in order to be able to get the LED drivers in and out for these ceiling high-hats. I now have to be pro-active as many are furring out the ceilings to get the high-hats in. Thoughts? Would you allow this on a post tension slab?

IMG_5844.JPG
 
I don't think so.
Cutting into PT slabs and floors happen all the time. As e hilton stated, you need to have ground penetrating radar to determine where the cables are (and any other embedded items such as conduit) before drilling or cutting. No drilling or cutting can happen unless the structural engineer has reviewed the work, done the calculations, and given his/her approval.
 
I have no experience with GPR or x-ray. Using the example of a retaining wall I wonder if the GPR works for that and how detailed it will be. Can the size of rebar be determined?
 