I'm not seeing what you are seeing.Reduction of pipe size in direction of flow? from the 3inch toilet to 2 inch drain.
For waste, as there is no "propulsion" you might get buildup there as nothing "pushes" or directs downstream.....If it were a vent connection it would be fine...oh i thought lav meant it was a toilet. i guess it's just a sink, huh? what do you think is the intent of not having a sanitary tee there?
1. Helps reduce trap siphonage, air locking, and turbulence by allowing more air into the system. Best example of this is to take a 2 liter bottle or similar container, take the lid off, and point it straight down. The water will not pour out as effectively as if you turn the water bottle to 45 degrees, there will be a lot of glugging and you will see the bottle vent itself with individual large bubbles of air that create a very turbulent flow. The shallower your angle is, the smoother the flow will be and ultimately the container will empty itself faster.oh i thought lav meant it was a toilet. i guess it's just a sink, huh? what do you think is the intent of not having a sanitary tee there?
There are no practical difficulties in new construction where framing and plumbing could have been coordinated. Their lack of coordination and last-minute changes do not justify simple minimum code requirements.Personally I would have let it go. Look at the limited room, he had to use a street elbow and turn it down to get below the floor joist before the floor beam.
Is it a code violation? Yes. Will it work for one sink? Yes.
View attachment 15187
[A] 105.1 Modifications.
Where there are practical difficulties involved in carrying out the provisions of this code, the code official shall have the authority to grant modifications for individual cases, upon application of the owner or owner’s authorized agent, provided that the code official shall first find that special individual reason makes the strict letter of this code impractical and the modification conforms to the intent and purpose of this code and that such modification does not lessen health, life and fire safety requirements.
I agree however when there is a lack of coordination and a simple code requirement is violated do you look for solutions or insist on compliance with the code.There are no practical difficulties in new construction where framing and plumbing could have been coordinated
Yes, the solution was figured out by the plumber, and the job is now compliant. I am not here to be a crutch to those who don't plan in advance and can't meet simple minimum codes. The plumber understood and actually knew in advance they were going to fail but was waiting to see if I would catch it, which I did. He already knew what had to happen to fix the code violation. I don't like being an enabler. However, I am willing to work with contractors on real issues that have difficult situations for compliance. This was not one of those times. This way, I won't hear the following words in 6 months: "You let me do that on the last job."I agree however when there is a lack of coordination and a simple code requirement is violated do you look for solutions or insist on compliance with the code.
OK, but the lav could have followed a similar route and joined the 3" drain on the horizontal below the joists.Personally I would have let it go. Look at the limited room, he had to use a street elbow and turn it down to get below the floor joist before the floor beam.
So did they do one of the above 3 things, or something else I didn't think of?Yes, the solution was figured out by the plumber, and the job is now compliant.
Gotta watch the heel inlet:There's a couple other possibilities that might have worked: one is to change the quarter bend to a quarter bend with low heel inlet (aka 3x2x3 san-tee) and then route the lav drain to the low heel inlet; not sure there would be enough height in the joist bay for the lav drain routing.
Eh, that should not apply when the "low heel" inlet is vertical. There's no difference in the bend geometry between a 3x3x1-1/2 low heel inlet quarter bend and a 3x1-1/2x3 san-tee (i.e. a 3" san-tee with a 3x1-1/2 bushing in the straight inlet).P3005.1.2
Heel-inlet quarter bends shall be an acceptable means of connection, except where the quarter bends serves a water closet.
No. He made the connection above to a nearby stack above the floor line. There was a lot of room behind a false wall.So did they do one of the above 3 things, or something else I didn't think of?