Class a-4 distance from washroom

We do 500' and that would be less meters....

[P]​

In occupancies other than covered and open mall buildings, the required public and employee toilet facilities shall be located not more than one story above or below the space required to be provided with toilet facilities, and the path of travel to such facilities shall not exceed a distance of 500 feet (152 m).

Exceptions:

  1. 1.The location and maximum distances of travel to required employee facilities in factory and industrial occupancies shall be permitted to exceed that required by this section, provided that the location and maximum distances of travel are approved.
  2. 2.The location and maximum distances of travel to required public and employee facilities in Group S occupancies shall be permitted to exceed that required by this section, provided that the location and maximum distances of travel are approved.
 