Class IB storage amounts
Inspector 102
N/E Indiana
I have an industrial building that wants to store 55 gallon barrels of Class IB liquid as part of their process. It appears that Table 3404.3.4.1 (2006 IFC) allows 7500 gallons (136 barrels) in a sprinklered facility as long as the area is separated by 1-hr fire barrier wall protection. Am I looking in the right table for this use. I know that spill containment will also be required.
That table is for wholesale and retail occupancies only. The fact that you mentioned a "process" makes me think you may be in the wrong table. What exactly does this facility do?
This facility manufactures deck lids for farm machinery and other vehicles. it appears that Table IFC 2703.1(1) might be the applicable based on occupancy. This table would allow 240 gallons total (spk bldg.) which seems awful small when the other table would allow 7500 gallons storage. These will be closed containers, no pressure and moved to another location when used, 55 gallons at a time. Sprinkler already designed as Ordinary Hazard, group 2 and plans for 8" diking around the room is planned for secondary containment. I would my fire inspector for assistance, but in the past he has told everyone to call me for the answer. I am reaching out for guidance. Thanks
Table 2703.1.1(1) is designed to give you the maximum quantity per control area to NOT be classified as an H use. Are they spray painting?
Don't forget that if they store in accordance with 2703.1.1(1) footnote e they get another 240 gallons for a total of 480 gallons per control area, and on the first floor they can have 4 control areas at 100% of that quantity (IBC 414.2.2), so they could have 1,920 gallons.
Tabular = 120
+100% for sprinklers = 240
+100% for storage in approved storage cabinets, day boxes, gas cabinets, exhausted enclosures or safety cans = 480 each control area
Ordinary Hazard Grp 2 is not adequate more like Extra Hazard Grp 2, see NFPA 13, 2007 ED below
5.4 Extra Hazard Occupancies.
5.4.1* Extra Hazard (Group 1). Extra hazard (Group 1) occupancies
shall be defined as occupancies or portions of other
occupancies where the quantity and combustibility of contents
are very high and dust, lint, or other materials are
present, introducing the probability of rapidly developing
fires with high rates of heat release but with little or no combustible
or flammable liquids.
5.4.2* Extra Hazard (Group 2). Extra hazard (Group 2) occupancies
occupancies with moderate to substantial amounts of flammable
or combustible liquids or occupancies where shielding
of combustibles is extensive.
A.5.4.1 Extra hazard occupancies (Group 1) include occupancies
having uses and conditions similar to the following:
Aircraft hangars (except as governed by NFPA 409, Standard
on Aircraft Hangars)
Combustible hydraulic fluid use areas
Die casting
Metal extruding
Plywood and particle board manufacturing
Printing [using inks having flash points below 100°F (38°C)]
Rubber reclaiming, compounding, drying, milling, vulcanizing
Saw mills
Textile picking, opening, blending, garnetting, or carding,
combining of cotton, synthetics, wool shoddy, or burlap
Upholstering with plastic foams
A.5.4.2 Extra hazard occupancies (Group 2) include occupancies
Asphalt saturating
Flammable liquids spraying
Flow coating
Manufactured home or modular building assemblies (where
finished enclosure is present and has combustible interiors)
Open oil quenching
Plastics processing
Solvent cleaning
Varnish and paint dipping
Product: Dicyclopentadiene
Flammability: Class IB Liquid
Boiling Point: 170.7 ºC
Flash Point: 32.2ºC
The number of barrels is around 40 barrels. The more I dig on this, the deeper I seem to go. It appears that the area will be H-3 occupancy and require 2-HR wall separation from F-2 existing occupancy. The sprinkler system existing is .15 @ 3000 SF so the system will need to be changed. With those changes it appears that the allowable storage amount is now 15,000 gallons (ground floor) based on IFC Table 3404.3.6.3(3). I will be passing this back to the owner and telling him that a design professional needs to review the storage area and submit code data and requirements but would still like to follow this closely for my own knowledge. It just seems that the code has bounced back and forth will no clear requirement. Have not dealt with one of these for a long time and brain has obviously gone to mush.
102
Very good research
Away from the book a few more days so do not know what the table or section you sited says
Normaly once you go H you are unlimited in storage amount
Also a way not to be H is to store max allowed inside and anything over that outside
In my research I have come up with the following basic guidelines
Flash Point: 32.2ºC
Classification of Storage Area H-3, High Hazard
Separation Requirements from F-2 Occupancy 2 Hour Separation
Allowable storage in gallons 15, 000 (272 drums)
Sprinkler Coverage Extra Hazard Group 2
Opening Protection 1 ½ Hr- Rated protection
Spill containment requirement Containment required
Portable fire Extinguisher 20-B Rated within 10 feet of door
This appears to be the reasonable route to go since a control area will only allow 240 gallon (480 in cabinet) which does not work for the amount they need to keep on hand. It seems strange that a wholesale or retail M could allow 7500 gallons in a control area with 1-HR barrier and sprinkler protection but an F-2 is so limited. They expect to have 80 barrels maximum on hand at any given time so this should work for them. I am still advising them that a design professional needs to review and submit changes and that way I am protected and the insurance company is satisfied. Thanks for the comments
If I'm not mistaken they are permitted to have (4) control areas and MAQ with footnotes in all (4) control areas. There is another one of those %$#@ tables that will even reduce the separation down to 1 hour if the sprinkler system is designed to EH1
I considered the control areas as a recommendation for their product. I think with the amount, they would be looking at a greater expense with 4 control areas than one H-3 area. I will let them make that call but thanks for the heads up.