Excellent. Glad that one went the right direction.Just an update.
I had a meeting with the owner. It went well. I explained everything to him and what I needed for acceptance. He acknowledged it and said he would get back to me.
Today, sitting on my desk is his revised set of plans and the specifications sheets with test results showing that this material has passed NFPA 701 test method 1.
Now I feel better and I can approve this plan.
Fairly common in the clean room worldExcellent. Glad that one went the right direction.
Don't see too many membrane structures....especially not ones internal to another building.
I'd agree with that...Fairly common in the clean room world
How about compliance with 3102.3??
Hang up......... Section 3102 covers membrane structures.
3102.3 Type of construction
Noncombustible membrane structures shall be classified as Type IIB construction. Noncombustible frame or cable-supported structures covered by an approved membrane in accordance with Section 3102.3.1 shall be classified as Type IIB construction. Heavy timber frame-supported structures covered by an approved membrane in accordance with Section 3102.3.1 shall be classified as Type IV construction. Other membrane structures shall be classified as Type V construction.
Exception: Plastic less than 30 feet (9144 mm) above any floor used in greenhouses, where occupancy by the general public is not authorized, and for aquaculture pond covers is not required to meet the fire propagation performance criteria of Test Method 1 or Test Method 2, as appropriate, of NFPA 701.
3102.3.1 Membrane and interior liner material
Membranes and interior liners shall be either noncombustible as set forth in Section 703.5 or meet the fire propagation performance criteria of Test Method 1 or Test Method 2, as appropriate, of NFPA 701 and the manufacturer’s test protocol.
Exception: Plastic less than 20 mil (0.5 mm) in thickness used in greenhouses, where occupancy by the general public is not authorized, and for aquaculture pond covers is not required to meet the fire propagation performance criteria of Test Method 1 or Test Method 2, as appropriate, of NFPA 701.
Per rkect post with the update, it meets NFPA 701 Test Method 1. In that case, it also meets 3102.3.1, and per 3102.3, can be classified as II-B construction.Just an update.
I had a meeting with the owner. It went well. I explained everything to him and what I needed for acceptance. He acknowledged it and said he would get back to me.
Today, sitting on my desk is his revised set of plans and the specifications sheets with test results showing that this material has passed NFPA 701 test method 1.
Now I feel better and I can approve this plan.