Re: College dormitory "lounges" open to the rated exit corridor
Corridors are bounded by partitions. In the case of rated corridors, those are fire partitions [see IBC 708.1]
A functional area is not necessarily a room. Functional areas which are open to the corridor (i.e. not separated by a door) are part of the corridor and the fire partition bounding the corridor extends around these areas as well. This is the case with waiting areas, alcoves, etc.
Put a door between the functional area and the corridor and it becomes a room and cannot intervene (aka be within the bounding fire partitions) unless it specifically allowed.
In other words, you cannot subdivide the corridor (as bounded by the fire partition) into rooms (other than lobbies, etc.), but corridors can and do contain functional areas...like the lounges in the original post or as in a hospital where corridors are designed to hold equipment and patients.
My take on the case of functional areas containing toilets, if there's no door (such as you might find in a large facility like a stadium) then it can be within the bounding partitions of the corridor...though there may be other issues related to HVAC.
In my mind the big concern is slowing the spread of a fire which develops in an enclosed area to the corridor. If there's a door which might contain the fire and allow it to develop, then the wall which the door is in must be rated.
It's not a sore subject.cda said:brudgers So are you saying there is no such thing as a corridor???
Or what is your take on rooms connected to a corridor??
I know coming form u code background, that this is a sore subject from way back.
Just trying to build to some minimum standard
Corridors are bounded by partitions. In the case of rated corridors, those are fire partitions [see IBC 708.1]
A functional area is not necessarily a room. Functional areas which are open to the corridor (i.e. not separated by a door) are part of the corridor and the fire partition bounding the corridor extends around these areas as well. This is the case with waiting areas, alcoves, etc.
Put a door between the functional area and the corridor and it becomes a room and cannot intervene (aka be within the bounding fire partitions) unless it specifically allowed.
In other words, you cannot subdivide the corridor (as bounded by the fire partition) into rooms (other than lobbies, etc.), but corridors can and do contain functional areas...like the lounges in the original post or as in a hospital where corridors are designed to hold equipment and patients.
My take on the case of functional areas containing toilets, if there's no door (such as you might find in a large facility like a stadium) then it can be within the bounding partitions of the corridor...though there may be other issues related to HVAC.
In my mind the big concern is slowing the spread of a fire which develops in an enclosed area to the corridor. If there's a door which might contain the fire and allow it to develop, then the wall which the door is in must be rated.